Discuss RCD test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jbroady

Did an RCD test on a new consumer unit, but got a fail on 1 times, but passed on 1/2times & 5 times.
Thought it may just be the rcd so i checked my instrument on the second rcd, but was perfect.
So then i swapped the rcd over & tested again but same happend again failed on 1 times but passed on 5 times.
All mcbs are switched off, & i tested at supply side of the rcd.
Any ideas??
 
Did an RCD test on a new consumer unit, but got a fail on 1 times, but passed on 1/2times & 5 times.
Thought it may just be the rcd so i checked my instrument on the second rcd, but was perfect.
So then i swapped the rcd over & tested again but same happend again failed on 1 times but passed on 5 times.
All mcbs are switched off, & i tested at supply side of the rcd.
Any ideas??

Think you have answered your own question.
Well ok....no...if it tripped on the other tests I assume you mean the load side.
The usual cause of a sluggish RCd is an inductive/capacative load still in circuit ,but if you say all MCB's off that cant be the case....
 
Last edited by a moderator:
Can you clarify exactly how you tested the RCD, you say it passed on this and failed on that. Do you mean it tripped on x half, didnt trip on x1, and tripped on x5, was it on 0 degrees or 180 degrees or both, and you should be testing it on the load side NOT the supply side. I dont mean to be negative, but dont want to guess or assume what it is you are asking.

Cheers........Howard
 
okay so i tested the rcd as normal at 1/2 times both degrees no trip (pass), then at 1 times both degrees no trip (fail) then at 5 times both degrees trip (pass) & sorry i tested on the load side.
 
okay so i tested the rcd as normal at 1/2 times both degrees no trip (pass), then at 1 times both degrees no trip (fail) then at 5 times both degrees trip (pass) & sorry i tested on the load side.

Are you sure no loads were in circuit.....anything with a capacitor fools the tester into giving a longer trip time.
 

Reply to RCD test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
564
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
480
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock