chloebear

I think I know the answer to this one - but could do with some clarification.

30mA RCD trips out at 51.8mSec on 1 times test & 38.7 on 5x Test values seem high to me - Domestic installation. Repeated the test 3 times just to make sure. RCD probably 11 years old and, of course, never had the test button pressed.
 
fine at x1. just in the 40mSec. at x5. although the x5 seems a tad slow
 

Reply to RCD Trip Time in the Australia area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K