Discuss RCD Tripped More Than Once In a Single Evening in the UK Electrical Forum area at ElectriciansForums.net

chicat

-
Reaction score
0
My RCD tripped more than once in a single evening.

When I went into my kitchen to investigate my appliances I noticed that my washing machine was left on (in pause mode).

Does anyone think the cause of the tripping could be the washing machine (especially when left turned on)?
 
If the machine has been paused and isn't doing anything, then it's unlikely to "out of the blue" set off the RCD. Usually a faulty dishwasher or washing machine will trip an RCD when part way through a programme as they switch something on. Having said that, I had a dw with waterlogged control board once and that was totally random.
 
Maybe something is nibbling on your cables.

Maybe build up of earth leakage over several appliances.

Maybe the rcds tripped so many times its become sensitive.

Impossible to say exactly
 
OP - Unfortunately "random" RCD tripping is a complete pain and can be very tricky to locate and fix

I would suggest you keep a record of when it trips and what you had switched on at the time , and when you get a spark in show them the EICR you have done earlier this year.

Sorry if this isn't too helpful........
 
In my other thread wildwest posted this,

"Class II appliances ( look for a square inside a square symbol on the information plate) do not have an earth connection and so can be ruled out , unless they are being used outside and have developed an earth connection of their own, for example, a pond pump."

Am I right to assume that Class 1 and 3 appliances (like my microwave, kettle, dehumidifier) might be the cause? Thanks.
 
Last edited:
In my other thread wildwest posted this,

"Class II appliances ( look for a square inside a square symbol on the information plate) do not have an earth connection and so can be ruled out , unless they are being used outside and have developed an earth connection of their own, for example, a pond pump."

Am I right to assume that Class 1 and 3 appliances (like my microwave, kettle, dehumidifier) might be the cause? Thanks.

Could be fixed wiring or loads. For quick resolution an RCD tester and Earth leakage clamp are required plus someone who can operate those testers and interpret the findings.
 
In my other thread wildwest posted this,

"Class II appliances ( look for a square inside a square symbol on the information plate) do not have an earth connection and so can be ruled out , unless they are being used outside and have developed an earth connection of their own, for example, a pond pump."

Am I right to assume that Class 1 and 3 appliances (like my microwave, kettle, dehumidifier) might be the cause? Thanks.

Disagree with that ............. seen a broken SL single core tripping an RCD in mid air!
 

Reply to RCD Tripped More Than Once In a Single Evening in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock