Discuss RCD tripping at 1/2 x but not 5x in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

ngoodson1969

Hi all,

I have just changed a consumer unit for somebody. When I did the RCD test, they both tripped at half times and 1x but not at 5X.
Also, I had a call last night and they said that one side of the lounge lights causes the RCD to trip.
Any ideas please? Cheers.

Nick
 
First thing to do is rule your tester out as been at fault by borrowing one if results although odd are the same then its time to look at the rcd unit, were you testing through a circuit or directly on rcd unit.
 
Hi,

I went back today and fixed the problem, although not sure how I did it. It was a dimmer switch and I just re-tightened everything and it seemed to resolve itself.
I tested the RCD at a socket outlet.
 

Reply to RCD tripping at 1/2 x but not 5x in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
319
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
634
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock