Ok help before a pull out the rest of my hair got an rcd that trips when ring main breaker turned on got continuity but still trips when only live connected ant ideas
 
ok so just changed a board connected everything back up and was tripping on lights or so I thought so disconnected them. no all I have connected in board is two lives for ring main and rcd trips when ever I turn the breaker on
 
ok so got continuity not shorts insulation resistance low but not too low at 16meg and again all I have connected or two lives of the ring no neutrals for any circuit no earths for any circuit. RCD stays on until I turn the breaker on. Never come across a fault like it
 
IR test done with all earths connected? Sounds like you have a path to earth somewhere.

If there's a boiler or other fixed appliance on the circuit check for reversed polarity.
 
ok so got continuity not shorts insulation resistance low but not too low at 16meg and again all I have connected or two lives of the ring no neutrals for any circuit no earths for any circuit. RCD stays on until I turn the breaker on. Never come across a fault like it
With no Ns connected wont you have an imbalance in the circuit?
 
OP is saying he has only lives connected, energises mcb & then RCD trips. That 'lecky is going somewhere, and as already suggested there must be a parallel path to earth. Even 16 MΩ sounds like there's an issue somewhere, connected load or earth fault.
 

Reply to rcd tripping on a ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
443
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock