ok so got continuity not shorts insulation resistance low but not too low at 16meg and again all I have connected or two lives of the ring no neutrals for any circuit no earths for any circuit. RCD stays on until I turn the breaker on. Never come across a fault like it
Why would you energise without cpcs connected (let alone neutrals)?

This is not a safe way of fault finding.
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.
Stop repeating yourself, sign of old age.
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.

Could still be a neutral to earth fault......his cct neutral would have been at line potential as he had it disconnected from supply neutral lol.

Due to no reponses.......I imagine he has thrown the RCD'S in the bin, took the money and wheelspan off the driveway into the sunset!!!
 
Could still be a neutral to earth fault......his cct neutral would have been at line potential as he had it disconnected from supply neutral lol.

Due to no reponses.......I imagine he has thrown the RCD'S in the bin, took the money and wheelspan off the driveway into the sunset!!!
A bit drastic don't you think.:tongue::tongue::tongue:
 
I'd try IR between all 6 conductors bunched in one crock clip and all the other conductors in the installation, checking cpcs first.

Does it trip if you only connect that circuit whilst having all other conductors disconnected or isolated?
 

Reply to rcd tripping on a ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
443
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock