An RCD works on the balance of current flowing through it (only through the line and neutral). If you isolate the circuit via the MCB and then cut the cable, you will join the earth conductor and the neutral conductor, thus allowing some of the neutral current (from the neutral bar in the CU) to travel via the earth conductor in your isolated circuit.
This then causes an imbalance in the RCD and trips it off.

The reason why an RCD won't trip when you touch the casing of a metallic appliance, is due to not causing any imbalance of current through the RCD.
 
Classic case of overthinking the question.

@OP: Your original assumption (and hence the title) is wrong and misleading. Touching or cutting the CPC ('earth') of a circuit, regardless of whether the circuit is energised or not, does not trip an RCD. Therefore, there is no question to answer about why touching the case of an appliance does not cause this. As others have explained, it is making contact with the neutral that is the issue.

Re post 15, the assumption here is not correct either. If there is a potential between neutral and earth at the origin, e.g. with a TN-S system, even without load on the system the RCD might still trip when N & CPC are shorted by cutting the cable. If the installation has load on other circuits (which need not be on the same RCD or CU) it is more likely that there will be enough p.d. between N & E to pass a current above the trip threshold through the N-CPC short.
 

Reply to RCD tripping when earth core touched in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock