Hi guys I have come accross a weird problem, a cooker circuit fed by rcd two trips rcd 1 when cooker in use . Both rcd's changed , check neutrals etc replaced cable . Even took of rcd but still tripping the rcd! Help
 
List all your tests and results ... otherwise your wasting our time, without them we will all just be guessing.

Have you done a ramp test
Have you done a full RCD test
Have you insulation tested the associated circuit(s) to the rcd ??? Please give results and what circuits the rcd covers, have you disconnected physically the other circuits L & N to try isolate the issue if more than one circuit common to rcd.
Have you checked for crossed N in the board or borrowed N in the install

Please provide everything you can as it could be many causes and we end up going in circles.

Firstly though disconnect all circuits physically - adding the cooker first then try it, add each circuit there after until the problem re-occurs if not tripping with cooker only, possible N/E issue on unrelated circuit and the loading of the cooker is enough to show the issue.
 
Last edited:
Switch the cooker OFF switch all the boiling rings, oven and grills OFF and switch the cooker back on, now switch all the rings oven and grills back on one at a time until the RCD trips.
 
Hi guys I have come accross a weird problem, a cooker circuit fed by rcd two trips rcd 1 when cooker in use . Both rcd's changed , check neutrals etc replaced cable . Even took of rcd but still tripping the rcd! Help

Have you tried diss-connetting cooker 1 then testing cooker 2 ?
Could be something funny going on in cooker 1.

Remember the neutrals and earths must be 100% ok and seperate
Or the rcd's will do funny things.

One rcd could be more sensitive or quicker than the other.
 
Check for N-E faults anywhere in the installation, particularly on the side RCD1, cooker puts a big current through the N to the sub, this then causes N to rise with respect to E depending on the resistance of N this then causes an imballance to RCD 1 then click..
 
Check for N-E faults anywhere in the installation, particularly on the side RCD1, cooker puts a big current through the N to the sub, this then causes N to rise with respect to E depending on the resistance of N this then causes an imballance to RCD 1 then click..

Eh? You've got serious problems if the neutral is rising!

A N-E earth fault will simply divert a portion of the normal neutral current to earth via the fault. This is why an uncleared N-E fault can be very very dangerous
 
Going back to the OP am i right in thinking you are saying the cooker is installed on one side of a split db fed from an rcd and there is another rcd on the other side of the split board which is the one that is tripping? Is rcd 1 fed from rcd 2? Is the discrimination the correct way round?
 
Going back to the OP am i right in thinking you are saying the cooker is installed on one side of a split db fed from an rcd and there is another rcd on the other side of the split board which is the one that is tripping? Is rcd 1 fed from rcd 2? Is the discrimination the correct way round?

Yes he has said the cooker is supplied by one RCD but the other one trips when the cooker is used.

This is the normal and expected symptom of a N-E fault on one of the final circuits fed by this board (not necessarily the cooker circuit)
 
Back to basics testing required me thinks. Remember it's just electrics at the end of the day. It's a live a neutral and an earth. Ma dad loves saying that to me!!
 

Reply to Rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
580
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock