Discuss RCD tripping in the The Welcome Forum area at ElectriciansForums.net

A

AlarKris

I have a strange RCD tripping problem, we have a dual RCD consumer unit, when the main switch is turned off both RCD s activate, they have activated individually but not at the same time. There is no continuity between the neutrals and both sides have an insulation resistance of >25 meg, we have replaced both Rcds which are now Schneider , yet the problem still persists, everything tests fine. So I'm either missing something obvious or not, any help would be gratefully received, thanks
 
Hi and welcome to the forum.
 
Any recent DIY? Somebody been fiddling with the wiring.

It would be highly unlikely for what you outline without something significant being done!

Best you compare the test results from 6 months ago with now
 
Any recent DIY? Somebody been fiddling with the wiring.

It would be highly unlikely for what you outline without something significant being done!

Best you compare the test results from 6 months ago with now

we have they've not altered , barely at all, and no building work has taken place, the wiring is as we left it, you can see why we are stumped, I will ask about picture locations etc....
 
As we turn off the main switch both RCDs trip simultaneously, it's a bugger, nothing seems to have changed and the test results are good.
 
As above if the RCDs trip on main switch turning off then they just need to be turned on again before you switch on again.

However saying that when you switch off the main switch the RCDs trip so you have changed the RCDs is a bit like saying I turned the kettle on and the circuit breaker tripped, I have changed the circuit breaker and the kettle turning on still trips the circuit breaker.

Have you tried a new main switch?
 
Are you throwing the switch under normal load. Or have you tried it will all the ccts off and only the 2 rcds. As said earlier has the DP isolator been swapped out.

Me personally wouldnt get to hooked up on it. Just switch them back on again , as Richard said.
 
As you turn the main switch off, you break both L and N, but not both at exactly the same time. For a very short period of time (I'm talking a small fraction of a second here), perhaps you have the L still connected, but the N already broken.

Now imagine you have a circuit, or some connected equipment, with a low-ish insulation resistance from N to E. In normal operation, it doesn't cause a problem. But if only L is connected, and N is broken, perhaps enough current can flow (say 30mA) via the E instead, and cause tripping.

Have you checked IR, of N to E - both the installation and any loads that are connected when this problem shows up?

I had something like this recently where I could guarantee to trip the RCD with the main switch, turned out to be some lift shaft lights having low IR from N to E.
 

Reply to RCD tripping in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
341
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock