Tommy29

DIY
Reaction score
0
I have isolated the MCB feeding my garage when switched on trips the RCD. There is no load on the garage I have an internal switch in the garage that switches all circuits off. So the fault must be between the MCB and the garage switch. The armoured cable is under the patch so to dig up would be horrendous. Could it be a faulty MCB?
 
In short, the chance of this fault being a faulty mcb is so small, it’s verging on the impossible.

All this wet weather lately if I had to guess I would say water ingress is most likely.
You need an electrician to insulation test it first .
At least you will have a definite answer.
 
In short, the chance of this fault being a faulty mcb is so small, it’s verging on the impossible.

All this wet weather lately if I had to guess I would say water ingress is most likely.
You need an electrician to insulation test it first .
At least you will have a definite answer.
Thanks that’s what I has thought. I have checked insulation between Earth and Neutral and there is no indication of a short. I did not megger it only a multi meter.
 
I have isolated the MCB feeding my garage when switched on trips the RCD. There is no load on the garage I have an internal switch in the garage that switches all circuits off. So the fault must be between the MCB and the garage switch. The armoured cable is under the patch so to dig up would be horrendous. Could it be a faulty MCB?
Highly unlikely to be an mcb. I'd get someone to do a bit of testing for you, as changing random parts such as the mcb would be false economy. Is the switch in your garage single or double pole? If only single the fault cou,d be upstream of that rather than underground. But again testing would find this out.
 
Thanks that’s what I has thought. I have checked insulation between Earth and Neutral and there is no indication of a short. I did not megger it only a multi meter.
You haven't 'checked insulation' just lack of continuity. Multi meters tell fibs to the uninitiated, when it comes to IR. Needs L involved, too.
 
Last edited:
I'd be inclined to say you have an earth to neutral fault somewhere. As said above, wet weather. Has anything in the installation changed recently?
 
I have isolated the MCB feeding my garage when switched on trips the RCD. There is no load on the garage I have an internal switch in the garage that switches all circuits off. So the fault must be between the MCB and the garage switch. The armoured cable is under the patch so to dig up would be horrendous. Could it be a faulty MCB?
If the SWA cable is in fact under the patio, then the cement holding the paving down could have eaten through the cable. It happens!
 
15 minutes work, disconnect swa from both ends.
IR test the cable.

You will then know if the fault lies with the cable or in the garage installation itself.

At a guess, if it’s a normal garage with a socket circuit and a lighting circuit only, I would expect a decent spark that is used to fault finding should have a diagnosis within an hour.

If it’s an easy to find one, probably have it diagnosed and fixed within the hour.
 
If the SWA cable is in fact under the patio, then the cement holding the paving down could have eaten through the cable. It happens!
As davesparks stated the cement is highly unlikely to damage the cable. I've seen people get chemical reaction burns from cement/concrete its nasty stuff if it gets on your skin and reacts.
 

Reply to RCD TRIPS BUT MCB DOES NOT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
886
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
207

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock