A domestic customer has MK dual RCD board #1 and another BG dual RCD board #2 in loft.
On testing, a couple of circuits (32a & 16a radials) on board #2 had high Earth fault loop impedance ( over 3 ohms for a socket radial). I know that the BG board (in the loft conversion) does not really need dual RCD but interestingly by bypassing its RCDs EFLI drops by 1.4 ohms.

Has anyone seen such high resistances in BG RCDs ?
Has anyone seen high EFLI readings with 2x RCDs covering a circuit ?

BG technical have admitted that only a handful of RCD's have shown high loop readings & that by having 2x RCDs covering a circuit would induce a current in the RCD coil.
I have not noticed, however, that 2x RCD's downstream of each other have ever caused high readings in the past....any experiences/ views on this are welcome.
 
Its starting to be common and there has been a few posts re this issue.

Once you do a ZS bypassing the RCD you get a much lower result.

It was telectrix on the forum who had a ZS of over 350 ohms on a test and it turned out to be the resistance of the RCD.
 
Its starting to be common and there has been a few posts re this issue.

Once you do a ZS bypassing the RCD you get a much lower result.

It was telectrix on the forum who had a ZS of over 350 ohms on a test and it turned out to be the resistance of the RCD.

i wanted to test it's resistance to a lump hammer, but the customer wouldn't allow me to.
 
Tested a cooker circuit on a BG board yesterday, R1+R2 0.04 Ohms, Ze 0.10 Ohms

Text book value 0.14 Ohms.

Measured value was 0.68 Ohms.

Even allowing for a slightly high Megger MFT 'no trip' reading, there is still around 0.4 Ohms of internal impedance on this particular BG RCD.
 
Thank you all for your feedback..it is much appreciated.....it does seem that BG do have a known issue with this but like most will not admit is it a real problem. Maybe one day they might pay us for wasting our time on faulty products !!...then again ...... Hey, I just saw a pig fly over my house !!... I think it had BG on its ear...I need a beer.
 
From the sounds of things, if that pig had BG on it’s ear it would probably sh*t on you as it passed.
Am I being thick or something but I was under impression that if a manufacturer knows they have a production fault they were obliged to do something about it!

 
Last edited by a moderator:

Reply to RCD Upstream BG board HIGH LOOP impedance in the Australia area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock