Discuss rcd in the Australia area at ElectriciansForums.net

An RCD protects by constantly monitoring the current flowing in the live and neutral wires supplying a circuit or an individual item of equipment. Normaly, the current flowing in the two wires is equal. When an earth leakage occurs due to a fault in the circuit or an accident with the equipment, an imbalance occurs and this is detected by the RCD, which has a sensing coil inside which automatically cuts off the power before injury or damage can result.​
 
that explains the load side of the rcd but supply problems can cause trips, high ze on a tt i think, just wanted to know if this was poss
 
I think a high Ze on a TT will do this but only if you do not have an RCD as your main isolator. If it is a TT you are using, a higher Ze is permitted but not any higher than 100 ohms (a suggested resistance by Code of Practice for Earthing) and the isolator should have a 100mA rating to compensate for this.
 
From Understanding RCD´s by John Ware:

Operation of an RCD can occur due to a downstream fault such as a crossed neutral on a split-load board, high protective current or an upstream effect such as mains-borne disturbances.

Faults existing upstream of the RCD

13. A loose connection upstream of the RCD such as at the main switch or at the busbar connections can cause the device to operate.

14. Mains-borne disturbances such as spikes, voltage surges and dips, a lightning strike and the operation of distribution network switchgear and protective devices combined with capacitance to earth within the installation can cause unwanted RCD operation. A filter may be of assistance.

15. Site machinery or plant and installed services can cause mainsborne interference. Motors such as lift motors, control gear for discharge lighting and transformer inrush currents can cause unwanted RCD operation. Although significant transients can arise within an installation they would normally only occur under fault conditions. They might, however, travel to other installations where they could cause unwanted tripping of an RCD.

16. Overhead lines. Unwanted tripping may occur more frequently in an installation supplied by overhead lines compared to one supplied by an underground concentric cable. An underground concentric cable is, by its very nature, a good attenuator of transient overvoltages. Spurious tripping may be avoided by installing a filter upstream of the RCD at the origin of the installation.


http://---------------/Publish/WireRegs/WiringMatters/Documents/Issue19/2006_19_summer_wiring_matters_understanding_rcds.pdf
 
Last edited by a moderator:
yeah thanks, that was what i was looking for, i wonder if large barriers on train crossing near house could cause this?...........luke upstream being before installation, main fuse back towards transformer....
 
as above onit. its the outlaws house couple hundred yards from a main line crossing which has overheads aswell. Ive not looked at it yet just phone conversations:( tried the usual leaving lighting mcb's off, you know what its like over the phone talking to someone with no knowledge of electrics. Next door seems to be tripping alot though aswell. They left lighting mcbs off in the night to find the intruder batt went flat!no markings on mcb's!!
 
being the end users everything's up stream right up to the power station, therefore everything else is down stream from there...ye olde water analogy
 
Last edited by a moderator:
which way is upstream and down stream in the supply chain

cheers


Just to back up grey´s post:

Imagine an RCD was installed to the side of a current CU/DB (due to space constraints in the CU or the need to protect a new installed circuit to the 17th ect etc...) THEN UPSTREAM would be the cable taken from the CU, the CU to the meter etc etc...

Downstream would be the cable from the RCD for the circuit, the socket outlet (for example).

Think of it as a river - the source from the hill, downstream to the river, river to streams etc etc...
 

Reply to rcd in the Australia area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
662
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
883
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
478
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock