Discuss Recommendation request for Type B distribution board in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
13
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA.
Requirements:
  • 23 final circuits, so don't want to exceed an 8 way board - pref no higher than about 625mm.
  • SPD therefore not to steal 3 MCB positions but to sit alongside incomer.
  • Need AFDDs combined into single module with either MCB or RCBO depending on the circuit - don't wish to use a separate enclosure for AFDDs.
  • Decent quality but not unduly expensive whilst avoiding Chinese tat.
All the above could be met by Hager, except that their MCB/AFDD and RCBO/AFDD units (ARM9**U and ARR9**U) are only rated at 6kA and, Hager tell me, "are 6kA devices that have not been tested in a 3 phase installation or DB." Their planned ARL9**U series is not yet released but they say "will be suitable for 3 phase boards" despite being 6kA.
What suggestions could you fellows make, please?
 
FuseBox have just released a 3ph board with all the accessories - might be worth taking a look at and report back to us?
 
FuseBox have just released a 3ph board with all the accessories - might be worth taking a look at and report back to us?
Tried their website, seems rather short of detail. They offer a 7 way - but one way is robbed for the SPD, so too small - and 11 way but no detail on this whatsoever, not even dimensions.
I've been dealing with a Fusebox CU installed by someone else and am under impressed - poor alignment of mounting rail with case, so had to almost completely dismantle it to get lid to fit without undue pressure on the devices.
I was rather hoping that one of you fellows would have glanced at my wish list and said "brand X will do that".
 
I was rather hoping that one of you fellows would have glanced at my wish list and said "brand X will do that".

From the opening post one might get the impression that your wish list consists solely of Hager Invicta, but clearly that isn't going to fit the bill on this occasion.

Some compromises will need to be made and you'll have to determine whether those compromises can be made on size, price or perceived quality. Availability of AFDDs is probably going to reduce options considerably.
 
Height of Fusebox 11 way is 812mm according to paper catalogue . Know what you mean about alignment with their domestic boards, I do fit them as pretty much standard though as excellent vfm and so far zero out of box failures...(I'm looking at you Crabtree..) I've taken to trial fitting cover with devices on rail before termination to fine tune the fit before end of day frustration.
 
Just looked at their website and full specs are available for the whole range. Availability may be an issue as they are currently in the process of being released and I don't see an AFDD option for these boards as yet.
you are right no AFDDs available in paper catalogue either, although it does say 'TPN boards will accept FuseBox 6kA devices without any modification or additional hardware'...make of that what you will...
 
Just out of interest, why are you specifying AFDDs?
This is a village church where the major part of the heating is from quartz/IR radiants at wall plate level, thus the wiring is at height. The concern is that connections up there will never be checked at any subsequent EICRs due to access limitations, thus increasing the risk of fire at some future time, so prudent to fit AFDDs while we can.
And yes, in the normal course of events I would resist such manufacturer-imposed novelties. (Ducks back under the parapet.)
 

Reply to Recommendation request for Type B distribution board in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Need to source Type B 3-phase distribution & 3P MCBs for EVSE, 1P RCBOs etc. so my sparky can install. A 6-way 3P board will suffice. Wondering...
Replies
23
Views
3K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
As currently got sod-all to do, I was thinking about the choice of TPN board for a new set up. It only needs 2-3 three phase circuits and around a...
Replies
4
Views
2K
Hi, A relative has moved into a flat with a mid-80's Square D QO1 12F distribution board, which has MCBs on all outgoing ways. There are...
Replies
21
Views
10K
Apologies for the complexity of this question, but there’s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock