Discuss RECOMMENDATIONS FOR A TIME PERIOD FOR FIRE ALARM TEST in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Brunel

-
DIY
Reaction score
2
I live in a block of 8 privately owned flats, the maintenance is carried out by a private company.

We have a fire alarm system comprising of, smoke detectors, break glass call points, sounders and of course an alarm control panel.

As far as I am aware a full test of the system has not been carried out for over 24 mths.

1. Is there a recommended time period for testing?

2. Is there any statutory body I can contact? or any recommendations of how to put pressure on the maintenance company?

Thanks.
 
The system should have a full test every 12 months however the full 12 months should not pass without an intermediate test say at 6 months which should consist of testing at least one point on each zone. The system should also be routinely tested every week.
 
Both the Fire safety reform order and BS5839 give recommendations on testing and maintenance.
This guide from the fire and security association section of ECA provides some information. However do note that the regulations have been updated since this guide was published.
However if the fire detection system is in parts of the flats then access for maintenance can be difficult.
 

Reply to RECOMMENDATIONS FOR A TIME PERIOD FOR FIRE ALARM TEST in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
693
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
Replies
6
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all Just a quick one. For a fire alarm loop addressable system. Fp200 1.5mm cpc 1.5mm To obtain R1+R2 would you treat the "loop" as a...
Replies
3
Views
2K
Hello, I applied for a retrospective completion certificate for kitchen relocation. The work was done about 7 years ago. The building standard...
Replies
26
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock