Discuss recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

pepparz

on a schedule of circuit details for a installation certificate, under the circuit conductors cpc size in mm², what should be recorded when a SWA cable has been used but one of the inner conductors is used as the cpc (say single phase circuit supplied by 2.5mm² 3 core, 1 x phase, 1 x neutral, 1 x earth). should the cpc be recorded as the armouring or the 2.5mm² designated cpc conductor?
I personally think it should be the 2.5mm² designated conductor and not the armouring, which is the earth by default.
 
agree with that, as the armour is not always used as cpc, although it must be earthed.
 
On a two core you would declare the armour as the CPC size. If using a 3rd core and the armour both as your CPC, would you not aggregate the two sizes?

If you are just earthing the armour at one end then just the core size would be the CPC
 
On a two core you would declare the armour as the CPC size. If using a 3rd core and the armour both as your CPC, would you not aggregate the two sizes?

If you are just earthing the armour at one end then just the core size would be the CPC

but when would you design and install a circuit which needed both the armoring and a inner core to be the cpc. surely the cable should comply with just the inner core been the cpc?
 
but when would you design and install a circuit which needed both the armoring and a inner core to be the cpc. surely the cable should comply with just the inner core been the cpc?

it must comply if the cpc core is the same size as the line conductor. the point is that on your sotr, there's just room in the box to enter the core size e.g.2.5. where in hell are you going to fit "22mm steel armour having an equivalent copper size of 3mm"?
 
it must comply if the cpc core is the same size as the line conductor. the point is that on your sotr, there's just room in the box to enter the core size e.g.2.5. where in hell are you going to fit "22mm steel armour having an equivalent copper size of 3mm"?

ive got the schedules of about 20 DB's and the cpc size has been entered as "ARM"
 
ive got the schedules of about 20 DB's and the cpc size has been entered as "ARM"
I would say that would be OK for a two core cable without a core used as the cpc, if there is a core as the cpc then that is the size of the cpc, though I suppose you could say 2.5+armour, but this would not be totally according to the regs as you cannot use a combined mix of materials and sizes to meet the cpc requirements.
 
...... you could say 2.5+armour, but this would not be totally according to the regs as you cannot use a combined mix of materials and sizes to meet the cpc requirements.

I always believed the regs did allow this, certainly the mix of cable & sheath (armour) to meet the CPC is my interpretation of 543.2. And by default Ive always assumed that this (copper & steel) allows different materials/sizes to be used unless there is another reg I've overlooked?
 
New posts

Reply to recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
980
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock