Search the forum,

Discuss Reduced Neutral Sizing in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi, just want to check something. I am on a facility which has a 4 core 70mm non armoured feed from the transformer, coming into the DB at the other end it is now a 4 core 25mm non armoured cable (obviously it has a joint somewhere) and the earth conductor is from an unknown source, but both of these cables have reduced neutrals and the later is less than 50% the phase conductors.

I am planning to change the cables, but just wondering if anyone has seen reduced neutrals that small before?
 
You need to figure out where the transformer feed goes to
could it be a distribution board or LV metering and fuse?
 
N conductor at 50% of phase conductors is 'OK' although it does assume a balanced load and little neutral current, also assumes a sensible lack of neutral harmonics - so conductor size/s at each point can be excused. However as @James points out, logically there has to be a reason for the reduction in sizes so before working out if your neutral is up to the job you first need to know the entire story - if it's as simple as a joint and reduction in ongoing csa then clearly this isn't acceptable regardless of discussion on Neutral sizing. If you need a reminder, In = sqrt (Ia^2+Ib^2+Ic^2) - (IaIb+IaIc+IbIc)
 
You need to figure out where the transformer feed goes to
could it be a distribution board or LV metering and fuse?
You need to figure out where the transformer feed goes to
could it be a distribution board or LV metering and fuse?
It goes to a DB from the transformer, but as I say it starts off as 70 and ends up as 25, so there must be a joint somewhere underground
 
N conductor at 50% of phase conductors is 'OK' although it does assume a balanced load and little neutral current, also assumes a sensible lack of neutral harmonics - so conductor size/s at each point can be excused. However as @James points out, logically there has to be a reason for the reduction in sizes so before working out if your neutral is up to the job you first need to know the entire story - if it's as simple as a joint and reduction in ongoing csa then clearly this isn't acceptable regardless of discussion on Neutral sizing. If you need a reminder, In = sqrt (Ia^2+Ib^2+Ic^2) - (IaIb+IaIc+IbIc)
Thanks, thats was what I thought, just needing confirmation. The max is 160A, 200A & 140A and Neutral 130A, ave are 45A, 80A & 40A with 37 on the Neutral., so its not balanced, that is not to say that this was not so when it was installed. Some of these supply and distribution cables have been in for up to 40 years.

I have managed to update about 1/3 of the camp in the last 18 months, but due to budget constraints I can not do everything straight away.
 

Reply to Reduced Neutral Sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
768
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock