New member, DIY homeowner here.
I bought a new in-ground 1HP 120v Harris pool pump (online) and had it installed by my pool maintenance company. A few weeks later it appears blown -- it hums when the power goes on -- but I removed the back and the shaft turns easily so I suspect wiring issues.
There is an outside breaker that has 2 breakers, both supplied by 120v lines, both of which appear to go to the line terminals on the mechanical timer. One of the load sides of the timer goes to the pump terminal point, the other is not hooked up.
Testing the load side of the breakers, one was loose and the reading on my multimeter flicked in and out, so I swapped another double breaker and tested output.
The thing I don't understand:
When I installed the new breaker, before I attached the load lines, I flipped the house breaker back on to test the outside breaker output. As expected, I got 120 volts between each output and neutral. Testing between the breaker outputs I got 240 volts.
BUT -- when I attached the load lines -- without the pump wired yet -- and tested the output, I still get 120 volts between each breaker load side and neutral, but I no longer get 240 between the loads -- the meter reads zero.
When I test at the terminal point where the pump would be installed -- one black wire and one white wire -- I get 120 volts...BUT if I flip EITHER of the two breakers off, I still get 120 at the terminal.
Can this be right?
Thanks in advance.
 
New member, DIY homeowner here.
I bought a new in-ground 1HP 120v Harris pool pump (online) and had it installed by my pool maintenance company. A few weeks later it appears blown -- it hums when the power goes on -- but I removed the back and the shaft turns easily so I suspect wiring issues.
There is an outside breaker that has 2 breakers, both supplied by 120v lines, both of which appear to go to the line terminals on the mechanical timer. One of the load sides of the timer goes to the pump terminal point, the other is not hooked up.
Testing the load side of the breakers, one was loose and the reading on my multimeter flicked in and out, so I swapped another double breaker and tested output.
The thing I don't understand:
When I installed the new breaker, before I attached the load lines, I flipped the house breaker back on to test the outside breaker output. As expected, I got 120 volts between each output and neutral. Testing between the breaker outputs I got 240 volts.
BUT -- when I attached the load lines -- without the pump wired yet -- and tested the output, I still get 120 volts between each breaker load side and neutral, but I no longer get 240 between the loads -- the meter reads zero.
When I test at the terminal point where the pump would be installed -- one black wire and one white wire -- I get 120 volts...BUT if I flip EITHER of the two breakers off, I still get 120 at the terminal.
Can this be right?
Thanks in advance.
Carter you have me a little confused. If a motor ever hums you are looseing a phase and the motor is single phasing. When you say you have just 120vac are you reading both wires to neutral or ground or are you reading phase to phase which should give you 240vac
 

Reply to Replacing pool pump: wiring from breaker box through timer to pump acting strange. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
757
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
909
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
589
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and...
Replies
3
Views
1K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock