Discuss Replacing pull chord light switch in the DIY Electrical Advice area at ElectriciansForums.net

Jake88

DIY
Reaction score
3
Hi all.

DIY question. I've gone to replace a broken pull chord light in my bathroom (switching off mains power at MCU and testing before touching with a Voltage Tester Pen).
IMG-20221230-WA0011.jpg
There are 2 exposed red wires from two separate sets of housing, an exposed earth wire and a neutral wire that is unexposed and passing from one set of cable housing to the next. This doesn't seem to me a standard set up and I'm unsure which red wire should go into Com and which into L1.

Photos attached.

Any help appreciated otherwise I'll just call a handyman.

Thanks
Jake
 
The blacks joined together are the neutral loop. There are actually two earths in the green/yellow sleeving which should ideally be separately sleeved to ensure correct connection at the earth terminal and to completely cover them. The two reds go across the switch it doesn't matter which way, all those conductors require enclosing into the back box of the new switch.
Good luck trying to secure the new switch to what's left of the ceiling.
 
Might be worth fastening a piece of timber above that, between the joists. It will be easy to fasten the new switch up then.
 
The red wire that brings power into the switch should ideally be connected to the 'com' terminal, and the red going off to the lamp should be 'L1', but, as westward says, it will work just as well either way.
 
The blacks joined together are the neutral loop. There are actually two earths in the green/yellow sleeving which should ideally be separately sleeved to ensure correct connection at the earth terminal and to completely cover them. The two reds go across the switch it doesn't matter which way, all those conductors require enclosing into the back box of the new switch.
Good luck trying to secure the new switch to what's left of the ceiling.
Thanks for your help. Much appreciated
 
The red wire that brings power into the switch should ideally be connected to the 'com' terminal, and the red going off to the lamp should be 'L1', but, as westward says, it will work just as well either way.
Thanks Brian
 

Reply to Replacing pull chord light switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
406
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
252
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
2K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
485
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock