Discuss Resistor across L-N in an adapter box. Possible or asking for trouble? in the UK Electrical Forum area at ElectriciansForums.net

Gurnatronics

-
Trainee
Reaction score
23
If I place say an 80 Ω resistor across L-N, would that generate a load of approx 2.8A.

I’m looking to create an artificial load of a socket circuit so I can locate the current at the DB using a clamp meter.

Used to use plug in 3kW heaters but not an option anymore, also definitely not able to isolate the power to test.

Thanks in advanced!! :)
 
If you want to put a load on a circuit... you can still buy 2kW fan heaters... what's wrong with them? Or a kettle?

Or as @grumpyjohn01 suggests, a circuit locator? Although it's not a precise science as the signal injected into the circuit will appear on others and at the board it can be a bit hit and miss.
 
If you want to put a load on a circuit... you can still buy 2kW fan heaters... what's wrong with them? Or a kettle?

Or as @grumpyjohn01 suggests, a circuit locator? Although it's not a precise science as the signal injected into the circuit will appear on others and at the board it can be a bit hit and miss.
Agreed, not an exact science but if you persist you can usually track the right one down. If you don't know which circuit a socket is on you may also not know if there are existing loads as well so in that case putting a known load on may not be an exact science either!
 
Forgive me if I sound stupid, but isn’t power dissipation a side effect of lower efficiency… ie heat losses?

Sort of, yes. It's got a very close relationship with voltage and curre t though.
 
I’m going to get one of those for that stately home testing job coming up.
I've got the 'socket & see' one ,originally acquired for a hospital testing job. As Sparkychick says they are not an exact science but the longer you scan for they reckon to filter out the weaker signals and eventually you are left with the right one. In my experience with a few other clues and your 'supersparky senses' you can usually get there in the end. Not so much of a problem if you can isolate to confirm but a bit more nerve-wracking in a medical environment..!
 

Reply to Resistor across L-N in an adapter box. Possible or asking for trouble? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
147
Hi everyone, hope you’re all doing well. Got a job starting next week for a rewire of a studio flat, currently they have 10 mm T&E as metre tails...
Replies
9
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock