Discuss resitance of 6mm t&e per meter. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

if you r talking about twin n earth i think the cpc is 2.5mm (4mm on 10mm TnE).

1m of 6mm copper = 0.01 ohm +

1m of 4mm copper = 0.017 ohm

this would total 0.027 ohm or i would round to 0.03 ohm
 
Hi,
If its 6mm line conductor and 4mm cpc then resistance would be 7.69 milli ohms per metre.

If its wrong, please let me know as I just checked on G3 page 104

Regards,Sav
 
The resistivity of pure copper is 1.7 × 10-8 W m3

resistance = resistivity × length divided by area (csa) Therefore;
R= rl
.....A

So a 6mm2 wire will be;
(1.7 × 10-8) x 1, divided by (6 x 10-6)
or (1.7 × 10-2) divided by 6
= 0.0028 W

or 2.8 mW

Alternatively you could use the tables in the OSG;:D


 
Last edited:
He was asking about T+E.....

Okay Ben Is this better?;)

1 metre of 6mm =

(1.7 × 10-8) x 1, divided by (6 x 10-6)
or (1.7 × 10-2) divided by 6
= 0.0028 W

or 2.8 mW

+

1 metre of 4mm

(1.7 × 10-8) x 1, divided by (4 x 10-6)
or (1.7 × 10-2) divided by 4
= 0.00425 W

or 4.25 mW

Total = 2.8 + 4.25

= 7.05 mW
 
Okay Ben Is this better?;)

1 metre of 6mm =

(1.7 × 10-8) x 1, divided by (6 x 10-6)
or (1.7 × 10-2) divided by 6
= 0.0028 W

or 2.8 mW

+

1 metre of 4mm

(1.7 × 10-8) x 1, divided by (4 x 10-6)
or (1.7 × 10-2) divided by 4
= 0.00425 W

or 4.25 mW

Total = 2.8 + 4.25

= 7.05 mW


C'est bon.:p:D
 

Reply to resitance of 6mm t&e per meter. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
427
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
915
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
847
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock