So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.
You can have a ring circuit and have no socket outlets at all if you want.So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.
What you save on cable you probably lose more on the junction boxes.Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.
You can have a ring with only j boxes if you want, and yes it's legal as you put it.If this situation arose is it legal. A ring with only jboxes is the point.
Do the junction boxes cost more than the cable you are saving?If this situation arose is it legal? A ring with only jboxes is the point. Or the actual ring cable with no sockets on it.
In #9 you stated big saving on cable.Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.
Thx. So OK to have a ring with no sockets on it.If you wish to design your own non-standard circuits then you are free to do so,
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.
As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.
What about the cost of the joint boxes or are you not going to answer that.The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net