I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on it which double up as junctions. I find that hard to believe.
 
Last edited:
A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.

Spurs do not have to be taken from sockets, they can be taken from a suitable joint box or from the origin of the circuit.


As always the above refers to the 'standard circuits' as described in the regulations and supporting publications. If you wish to design your own non-standard circuits then you are free to do so, however you would need to fully document the design (as a courtesy to anyone else who has to work on the installation, as defense should anything go wrong, as defense when an EICR is carried out and the non-standard design is flagged up, etc etc)
 
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.

No, it can't, not as a standard ring final circuit.

As I said, a ring can only have as many unfused spurs as it has sockets connected to the ring.

On your ring of cable with joint boxes, if you intend it to be a standard ring final circuit, you cannot have any spurs as you have no sockets on the ring.
 
What would lead you to design a circuit like this?

If you can get one cable to a socket, then you can get two.
It has no financial benefit, as the cable saving is countered by joint boxes and time making those extra joints.
The extra joints also add another point of possible faults.

In technical terms…. This is how a standard socket is. The joint is the terminals on the back of the socket… the “spur” is the internal metalwork between the terminal and the contacts for the plug pins.
 
Perhaps there is more to JSJW's design than he is letting on, but per post #6 what would be the point? Just as easy to accommodate sockets into the RFC!
 
Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.

As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.


Get your replies in now, lads…. Can’t see this thread lasting much longer. 😆
 
Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.

As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
 
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
What about the cost of the joint boxes or are you not going to answer that.
There are plenty of ring final circuits out there which do not incorporate socket outlets.
 
What about the cost of the joint boxes or are you not going to answer that.
There are plenty of ring final circuits out there which do not incorporate socket outlets.
I refer you to post 19.

"There are plenty of ring final circuits out there which do not incorporate socket outlets."

Getting somewhere.
 
I refer you to post 19.

"There are plenty of ring final circuits out there which do not incorporate socket outlets."

Getting somewhere.
Where are we getting. Ring final circuits without sockets outlets have been around since the advent of the ring final.
 
The regs don’t state sockets, they will state points.

The regs concerning unfused spurs comes from the load on the spur not being too much for the cable between the ring and the point.
How that cable is joined into the ring is immaterial. Joint box, or back of another point.


That is from memory, as it’s Sunday and I can’t be bothered to look for my book.
 
The regs don’t state sockets, they will state points.

The regs concerning unfused spurs comes from the load on the spur not being too much for the cable between the ring and the point.
How that cable is joined into the ring is immaterial. Joint box, or back of another point.


That is from memory, as it’s Sunday and I can’t be bothered to look for my book.

Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.
 
Any fridge is on 24/7/365, but still comes with a plug fitted.
But there is nothing wrong with hardwiring them into a switch fuse.... its just not standard
Basically, if its stuck to the wall, it doesnt come with a plug..... if its portable... it does.
And portable does include large, american style fridge freezers.

Either way, whether an appliance is plugged in or not isn't part of the original question.

Which, if i understand it, was

"can you just have a ring circuit, with no points on the ring itself, but unfused spurs coming off the ring, with points on the end of each spur"

And a very early answer was "yes, but it would be non-standard"
There's nothing in the regs to say you cant.
 
Was common place back in the 70s often known as a 'spider ring' all ran around to circular junction boxes with radials to each accessory it isn't anything new. Some dwellings had the ring final on the upper floor with accessories connected with spurred radial drops to the lower floor.
 
A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.
I used to believe this too. I don't know if it was included in the 15th or 16th edition, but there's no mention of it in BS7671:2018+Amd2:2022 (at least as far as I can see).
 
Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.

And then, when the homeowner needs a new fridge, he has to get a sparky out to disconnect the old one and reconnect the new one.

Makes perfect sense to use a plug, especially since it will come with a pre fitted one.
 
Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.

Assuming the average ring circuit has 10 sockets on it and you save 3m of cable per socket that's a saving of 30m of cable.
At current prices that could be about £25 saved.

Depending on your preference for joint boxes they could realistically cost you £25.
Then you need to consider the additional time involved.

Other considerations are best practice, it is generally accepted that best practice is to avoid unnecessary joints in cables, every joint being a potential point of failure.

Also you need to consider maintainence and fault finding, it is going to be a lot harder to fault find a ring circuit where you can't readily get to the ring itself.
 
Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.

Why not? Sockets are for any appliance regardless of how often it needs to be connected/disconnected.

This is especially true in domestic installations where small appliances, white goods, etc will often be connected/disconnected by untrained or unskilled people.
 
Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.
So why do some manufacturers consider removal of the plug from the socket is safe isolation of the appliance when they need to carry out warranty work. Back to the old you can't cut the plug off without voiding the warranty debate
 
Last edited:
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.

The point of a ring final circuit, the whole reason it was created in the first place, is to supply multiple, general use sockets over a relatively large area as efficiently as possible.
The point of the ring final circuit is to have the flexibility to supply multiple loads which are generally unknown and generally moveable.
The design of the standard ring final circuit is based on certain assumptions, including the assumption that loads will be relatively evenly distributed

If you are installing a dedicated appliance circuit what would be the point of installing a ring circuit? The loads are known at the design stage, a dedicated appliance circuit can be designed to cater for the appliances and has no real need to be a ring.
 
Read the beginnings of this thread last night and its aim is less than clear.

Initially the OP expressed disbelief that a ring could not exist for the sole purpose of providing a source of power for spurs. This was cleared up by @davesparks who pointed out the rules which apply in terms of the number of allowable spurs and their dependence on the number of sockets in that ring and that a ring can not simply exist as a form of busbar, from which sockets can be spurred.

We then have a suggestion from the OP of a ring serving as a busbar for heavy appliances, which brings us back to the point from previous, similar threads about ring final circuits and how the OP's thinking fails to take other regulatory limitations into account.

While I do think there's merit in the idea of such a busbar, it could never exist in practice (in a domestic installation) if one is to meet all regulatory requirements. In some regards I applaud the OP's inclination to think 'outside the box', but that tendencey to think is severely hampered by an apparent inability to 'see the bigger picture'. Surely anyone familiar with BS7671 would see the numerous problems such a proposal poses and not just the one potential benefit? This isn't the exploitation of a loophole the OP thinks it is, but a potentially huge headache for any homeowner who allows such an experiment in their home. I'm sure the OP would feel assured in their misplaced confidence to sign off such a departure from BS7671, but very much doubt they'd be prepared to bear the costs incurred when remedial work was required to resolve the obious issues likey to arise. This industry evolves through innovation, but sometimes it's better not trying to be clever and to simply work within the confines that a century of experience places upon us.
 
Whatever standard and non-standard are.

In this situation standard refers to the standard circuits described in bs7671 and associated publications. They are best described in the on-site guide I believe.
Standard circuits refers to the 32A ring final, 20A radial and 32A radial circuits described in those publications. Details are given for minimum cable size, maximum length of cable etc etc

Non-standard refers to any other circuit which you will have designed yourself.
 
Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.

Manufacturers have ensured that there's nothing permanent about fridges, nor any other white goods, and a fridge is one appliance that I'd never consider supplying from a ring in any new installation.

This one appliance is very likely to be the greatest source of trouble in your theoretical circuit, despite its relatively low power consumption, and for reasons you've failed to take into account.
 
Assuming the average ring circuit has 10 sockets on it and you save 3m of cable per socket that's a saving of 30m of cable.
At current prices that could be about £25 saved.

Depending on your preference for joint boxes they could realistically cost you £25.
Then you need to consider the additional time involved.

Other considerations are best practice, it is generally accepted that best practice is to avoid unnecessary joints in cables, every joint being a potential point of failure.

Also you need to consider maintainence and fault finding, it is going to be a lot harder to fault find a ring circuit where you can't readily get to the ring itself.
MF jboxes.
 
So why do some manufacturers consider removal of the plug from the socket is safe isolation of the appliance when they need to carry out warranty work. Back to the old you can't cut the plug off without voiding the warranty debate
Manufacturers come out with all sorts of nonsense at times
 

Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
809
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
269
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock