Discuss Ring main,going going gone in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
My tutors told me to use this as a rule of thumb and you shouldn't go wrong, for a ring final circuit "1 roll of 100m cable = 1 ring final circuit", if that's wrong I stand corrected, but my tutors swore by this rule of thumb.
Found this remark on another forum,using 100m, that ring main ain’t gonna go far.
I usually have 2 rolls on the go.
 
main thing is the number of sockets, and whether there are drops of 6 ft. odd or rises of 2 ft.
 
I suspect there has been some confusion here with the maximum floor area for a 32/30A ring final being 100m sq. It is possible they could also be referring to the volt drop limit if you only use 100m of cable in the circuit bit I am pretty sure that is too high as I thought it was 79m for a well balanced circuit.
 
also to do with the cable resistance .... Zs value. for a 32A MCB you need a R1+R2 < 1 ohm ( exact value depends also on Ze.). ain't got tables to hand, but from memory, 100m 2.5mm T/E wil give aroung 0.6 ohms for R1+R2.
 
Hi - another slant :) - is the tutor meaning "a ring circuit from a single 100m drum of 2.5/1.5 is unlikely to exceed the max loop impedance of a B32 RFC on a TNCS installation" (?) ... Is so, then I agree.

From the OSG Appendix I, 100m of cable R1+R2 is a bit less than 2 Ohms at 20 C.
So r1+r2 is a bit less than 0.5 Ohms at 20C.
TNCS Ze is less than 0.3 Ohms.
Total Zs less than 0.8 Ohms at 20C, or 1 Ohm at 70C, which readily complies with Table 41.3 for B32 OCPD.

For TNS the max Ze is 0.8 Ohms, giving a total of 1.3 Ohms max, which is close to the max of 1.37 Ohms.
 
It’s based on volt drop using 20A at the furthest point and the remainder up to the rating of the OCPD spread evenly. So for a 32A OCPD the design current is 26A. The mV/A/m for 2.5 is 18.

18x26x100=46800

46800/1000=46.8

46.8/4=11.7V

Just a Gnatscock over 11.5V which is the recommended, maximum, permissible value given in the regs of 5% of 230V for power. So the max is actually more like 98 meters but you easily loose the couple of meters when tidying the job up and cutting cables to tuck them into back boxes etc on 1st fix.
 
Last edited:
Hi - another slant :) - is the tutor meaning "a ring circuit from a single 100m drum of 2.5/1.5 is unlikely to exceed the max loop impedance of a B32 RFC on a TNCS installation" (?) ... Is so, then I agree.

From the OSG Appendix I, 100m of cable R1+R2 is a bit less than 2 Ohms at 20 C.
So r1+r2 is a bit less than 0.5 Ohms at 20C.
TNCS Ze is less than 0.3 Ohms.
Total Zs less than 0.8 Ohms at 20C, or 1 Ohm at 70C, which readily complies with Table 41.3 for B32 OCPD.

For TNS the max Ze is 0.8 Ohms, giving a total of 1.3 Ohms max, which is close to the max of 1.37 Ohms.
Wilko
Bit puzzled and not disagreeing in any way, but You mention R1+R2 for 100mts cable is less than 2 ohms.
Then in the next sentence r1+r2 is a bit less at 0.5 ohms both at 20degC.
It's probably me but can you explain what you mean ? sorry Mate just me wondering that's all.
 
Wilko
Bit puzzled and not disagreeing in any way, but You mention R1+R2 for 100mts cable is less than 2 ohms.
Then in the next sentence r1+r2 is a bit less at 0.5 ohms both at 20degC.
It's probably me but can you explain what you mean ? sorry Mate just me wondering that's all.
r1+r2 then divide by 4 because it’s a ring final circuit gives you R1+R2.

In the example above if R1+R2=2 Ohms

Then the expected value of r2 would be 2/1.67=1.19

Leaving 0.81 for r1

Obviously 1.19+0.81=2

2/4 because it’s a RFC gives you 0.5 for R1+R2
 
Just because the ring is a standard circuit and it's an easy to remember amount, there's nothing else special about the length of a roll. If you design it all correctly you won't end up far off so it's a rule of thumb.
It's just a short cut to avoid detailed design and calcs. You can just design a more suitable circuit if 100m isn't enough eg use 2.5mm or 4mm radials, or multiple rings, or even the feared lollipop circuit.
 
I think it is quite a useful , back pocket, reminder. I was wiring a large house that was a challenge for cable runs, UFH, high ceilings and the like. Client wanted sockets everywhere and i mean everywhere. Anyway when i had cabled 2 bedrooms and run off a 100m drum, i thought hang on and stopped the install. I ended up pulling in two extra SWA cables to SP Cu's just for VD and Zs. This house has ended up with 3 X TP boards and 2 X SP boards, not just because of socket wiring. its good to not just keep running more and more cable, something has to stop you and make you think. BTW at the design stage we did not have No of sockets and i did rather hope for easier shorter cable runs but in reality it was much harder.
 
If 543.2.9 is the one about conductors in ting finals being connected end to end then that still allows for a lollipop circuit. It's just that the ring is fed from another length of cable. Apologies if I've misunderstood your post.
 
There was some published 16th ed. electrical theory books that had some tables in them based on cable size, protective device and incoming earthing arrangements etc by Trever E. Marks.
 
If 543.2.9 is the one about conductors in ting finals being connected end to end then that still allows for a lollipop circuit. It's just that the ring is fed from another length of cable. Apologies if I've misunderstood your post.

That other length of cable would need to be to a distribution board - then the ‘circuit’ starts from there. I think the reg. refers to when people try to run a bit of cable into a junction box then start a ring from there - which is what the word ‘lollipop’ means to me. I think ‘lollipops’ are not allowed.
 
I think a circuit g fed from a feeder cable is allowed. Say for example a kitchen ring fed from a 6mm cable which feeds a now redundant Cooker outlet.
 
Not sure I agree with that .............

A lollipop circuit isn't a ring final circuit:)

Interesting - thanks Murdoch - but I think it’s more ring than radial. Why bother having two legs in a ring from that connection point? To share the load? To use smaller cable? If so - isn’t that what a ring is for.

I’ve recently had my scheme assessment - and my assessor was pretty adamant that the reg prevents lollipops. It’s certainly how it reads to me...

Must have been discussed before?
 

Reply to Ring main,going going gone in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
314
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
865
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock