disconnect both legs at the board, connect the line to the earth of one leg and check for continuity at the sockets themselves
I would do this. I wouldn't bother splitting the circuit. You installed it so you know the route it takes, follow one leg out, testing at each socket as you go. I'd use my R2 adaptor to speed things up.
 
I would do this. I wouldn't bother splitting the circuit. You installed it so you know the route it takes, follow one leg out, testing at each socket as you go. I'd use my R2 adaptor to speed things up.
Due to the run of the cable from the cu to the kitchen is restricts me from the r2 method so I was thinking if I connect the line to earth at the db of leg 1 at the board and then use my multifucntion tester with the plug attachment at each socket this should narrow the problem down?
 
Yes. Connect one leg to earth at the cu, disconnect the other leg too.
you can then do continuity tests between earth and line at each socket etc.
Blimey, don’t they teach people this basic stuff anymore?
(sorry, not having a go at you,specifically. )
 
Yes. Connect one leg to earth at the cu, disconnect the other leg too.
you can then do continuity tests between earth and line at each socket etc.
Blimey, don’t they teach people this basic stuff anymore?
(sorry, not having a go at you,specifically. )
No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying.
[automerge]1574627672[/automerge]
No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying. Cheers for the reply, appreciate it
 
Due to the run of the cable from the cu to the kitchen is restricts me from the r2 method so I was thinking if I connect the line to earth at the db of leg 1 at the board and then use my multifucntion tester with the plug attachment at each socket this should narrow the problem down?
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

[automerge]1574629153[/automerge]
Plug adaptor = R2 adaptor, same thing
 
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

[automerge]1574629153[/automerge]
Plug adaptor = R2 adaptor, same thing
I get you! Appreciate the response
 

Reply to Ring main no continuity on live ends in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
509
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
858
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock