A

andygosmore

It's obviously not good practice, but is there a specific reg prohibiting a 4mm from the board to a remote rcd a few metres away, & then a 2.5mm ring from the rcd, round the sockets then back to the rcd. I've come across it on a PIR, and unsure whether to pull it up or not.
Thanks
Andy
 
None as far as I can see. It doesn't feature as a conventional circuit in the OSG, but then if you do the sums and check the installation method and any other correct factors, it should be Ok.

I believe they call that type of circuit a 'loolipop'

A note on the PIR/EICR stating there are loolipops in the house should do it !
 
Last edited:
in effect the 4mm is just acting as a submain to the RCD and then a ring main off of it, this would be no different than an SWA going down to a remote RCD board in the shed and a ring main coming of of that,
as long as the calcs work out
 
It's obviously not good practice, but is there a specific reg prohibiting a 4mm from the board to a remote rcd a few metres away, & then a 2.5mm ring from the rcd, round the sockets then back to the rcd. I've come across it on a PIR, and unsure whether to pull it up or not.
Thanks
Andy

I can't remember the exact reg number, but I'm sure their is a requirement to fuse down at any point where their is a reduction in csa. From your description it sounds as though you only have an RCD locally protecting and not a fuse/mcb?
 

Reply to Ring main not originating in the DB. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
898
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock