Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Ring main not originating in the DB. in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. andygosmore
    Online

    andygosmore Guest

    It's obviously not good practice, but is there a specific reg prohibiting a 4mm from the board to a remote rcd a few metres away, & then a 2.5mm ring from the rcd, round the sockets then back to the rcd. I've come across it on a PIR, and unsure whether to pull it up or not.
    Thanks
    Andy
     
  2. ackbarthestar
    Offline

    ackbarthestar Forum Mentor

    Location:
    A Zoo near YOU
    None as far as I can see. It doesn't feature as a conventional circuit in the OSG, but then if you do the sums and check the installation method and any other correct factors, it should be Ok.

    I believe they call that type of circuit a 'loolipop'

    A note on the PIR/EICR stating there are loolipops in the house should do it !
     
    • Like Like x 2
    Last edited: Feb 21, 2012
  3. jase
    Offline

    jase Electrician's Arms

    in effect the 4mm is just acting as a submain to the RCD and then a ring main off of it, this would be no different than an SWA going down to a remote RCD board in the shed and a ring main coming of of that,
    as long as the calcs work out
     
    • Like Like x 3
  4. Engineer54
    Online

    Engineer54 Guest

    For futher reading on this subject, check out ''SIMILAR THREADS'' at the bottom of this page!!
     
  5. Dannyspark
    Offline

    Dannyspark Active EF Member

    Location:
    Wiltshire
    I can't remember the exact reg number, but I'm sure their is a requirement to fuse down at any point where their is a reduction in csa. From your description it sounds as though you only have an RCD locally protecting and not a fuse/mcb?
     
  6. GT1
    Online

    GT1 Guest

    2 x 2.5mm isnt a reduction in CSA from 4mm though..
    It's an increase in CSA.
     
    • Like Like x 1
  7. ackbarthestar
    Offline

    ackbarthestar Forum Mentor

    Location:
    A Zoo near YOU
    Because its ac it make sense that it would be oversized on the first half cycle and undersized on the second ?:dizzy2: :)
     
  8. ezzzekiel
    Online

    ezzzekiel Guest

    LOOLIPOP - i love it
     
Loading...
Similar Threads - Ring main originating Forum Date
Domestic Mapping existing ring main DIY Electrical Forum Jan 8, 2019
2 questions - Existing ring main mapping, and rules on spurs Electrical Wiring, Theories and Regulations Jan 8, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job