    It's obviously not good practice, but is there a specific reg prohibiting a 4mm from the board to a remote rcd a few metres away, & then a 2.5mm ring from the rcd, round the sockets then back to the rcd. I've come across it on a PIR, and unsure whether to pull it up or not.
    Thanks
    Andy
     
  2. ackbarthestar
    Offline

    ackbarthestar Trusted Advisor

    Location:
    A Zoo near YOU
    None as far as I can see. It doesn't feature as a conventional circuit in the OSG, but then if you do the sums and check the installation method and any other correct factors, it should be Ok.

    I believe they call that type of circuit a 'loolipop'

    A note on the PIR/EICR stating there are loolipops in the house should do it !
     
    • Like Like x 2
    Last edited: Feb 21, 2012
  3. jase
    Offline

    jase Electrician's Arms

    in effect the 4mm is just acting as a submain to the RCD and then a ring main off of it, this would be no different than an SWA going down to a remote RCD board in the shed and a ring main coming of of that,
    as long as the calcs work out
     
    • Like Like x 3
  4. Engineer54
    Offline

    Engineer54 Guest

    For futher reading on this subject, check out ''SIMILAR THREADS'' at the bottom of this page!!
     
  5. Dannyspark
    Offline

    Dannyspark Active EF Member

    Location:
    Wiltshire
    I can't remember the exact reg number, but I'm sure their is a requirement to fuse down at any point where their is a reduction in csa. From your description it sounds as though you only have an RCD locally protecting and not a fuse/mcb?
     
  6. GT1
    Offline

    GT1 Guest

    2 x 2.5mm isnt a reduction in CSA from 4mm though..
    It's an increase in CSA.
     
    • Like Like x 1
  7. ackbarthestar
    Offline

    ackbarthestar Trusted Advisor

    Location:
    A Zoo near YOU
    Because its ac it make sense that it would be oversized on the first half cycle and undersized on the second ?:dizzy2: :)
     
  8. ezzzekiel
    Offline

    ezzzekiel Guest

    LOOLIPOP - i love it
     
Loading...
Similar Threads - Ring main originating Forum Date
Ring main consisting of only spurs Electrical Wiring, Theories and Regulations Jul 1, 2018
Mains doorbell wiring Electrical Forum Jun 2, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job