Discuss ringmain testing in the UK Electrical Forum area at ElectriciansForums.net

S

sparkie-leeds

Hi,

I have just tested an existing ringmain starting with the line conductor reading 0.32 and the neutral reading 0.87, these are both in 2.5 twin and earth, can someone explain why there is a big difference in the 2 readings when the conductors are the same size?
 
None of the result sound correct, i'd re-test and see what you come up with. Make sure you have your test leads connected properly and nulled as suggested earlier
 
Looks like r1 is a little high too if your r2 is 0.28, its got loose connection written all over it or dodgy test leads mine gave me some funny readings the other day so I changed them now there perfect
 
so its an EICR is it?....if so then you cant sample on this circuit.....check all points served.....including any joint boxes.....
while your at it...make a note of any stuff like neons etc that will throw up silly IR readings later on.....unless you just test live to earth that is....
 
Don't forget that this is an existing installation, so the fact that r2 is lower than the r1 is understandable and most probably due to existing parallel earth paths. The r1 reading equates to approx 40-45 metres, so check if this is right.
although the rn reading is high and does suggest loose connections.
 
Don't forget that this is an existing installation, so the fact that r2 is lower than the r1 is understandable and most probably due to existing parallel earth paths. The r1 reading equates to approx 40-45 metres, so check if this is right.
although the rn reading is high and does suggest loose connections.

He's not put the r2 figure, just r1 and rn.

also shouldn't be any parallel paths on an end to end cpc test.
 

Reply to ringmain testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
679
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
664
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
428
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock