Discuss Routing of meter tails in the UK Electrical Forum area at ElectriciansForums.net

So what do you think that tells you Leep82
It doesnt tell me im wrong as its all opinion. No install method mentioned is a deviation from the Regs and nobody has said i shouldnt use T&E because of ........ My prefence would be SWA>T&E>insulated/sheathed tails, but it all depends on the installation.
 
It doesnt tell me im wrong as its all opinion. No install method mentioned is a deviation from the Regs and nobody has said i shouldnt use T&E because of ........ My prefence would be SWA>T&E>insulated/sheathed tails, but it all depends on the installation.

You not alone, I've seen quite a few such distribution circuits done with tw&e. If done correctly, there's nowt wrong with it. Prefer to allow using swa myself.
 
You can use T&E if you want.
The CPC will have to be a minimum CSA of 10mm2 if PME conditions apply.
Where the cable passes through joists or battens above a ceiling or below a floor, it will have to be a minimum of 50mm from the surface of the ceiling or floor, or provided with mechanical protection.
If it’s concealed in walls it will have to be at a minimum depth of 50mm or in a prescribed route and provided with 30mA RCD protection.
 
I wonder who is going to break the seals on the cut out and meter and remove the fuse in order to install the load tails and KMF unless there is already a double pole isolator fitted.
It is coming up to Christmas so perhaps the "Seal Fairy" :)
I guess the tails from the cut out to meter are also 25mm and fully tightened?
 
Last edited:
Yeah im not saying its by any means fool proof, i just feel theres more chance of striking more than just the one conductor when using a T&E

Actually with the theee separate single core cables properly bound in a triangular formation you’d be more likely to hit more than one core with a screw as they overlap better in all planes.

But ‘more likely to hit’ is irrelevant and offers no protection.
 
Without wanting to sound stupid what is tht earthed armour offering ?

That earthed armour is offering protection from electric shock for anyone damaging the cable with a metal object.
The point of having earthed armour on a cable is to connect any metal object which penetrates the cable to earth before it makes contact with any live conductor, this in turn ensures operation of the protective device.
 
You must have some means of protection at meter position, dno fuse is NOT acceptable, it is to protect the dno's system, not the installation.
 
That earthed armour is offering protection from electric shock for anyone damaging the cable with a metal object.
The point of having earthed armour on a cable is to connect any metal object which penetrates the cable to earth before it makes contact with any live conductor, this in turn ensures operation of the protective device.
Yes i agree, so by that token does a metal object have more chance of striking the CPC in a T&E than it does if using insulated/sheathed tails? Im not trying to argue against SWA, its the best method discussed on this thread. I was just asked what benefits a T&E would have over tails and for me this is it. Granted its by no means a certainty and as none of the install methods are not to current regulations it doesnt actually matter, but my personal opinion is the T&E method has advantages over 25mm tails
 
Apart from the use of SWA I think we are getting into the argument of good practice.This supply in "meter tails" should not be protected by the DNO protective device.
 
Would be my best case scenario too, if budget & circumstances allow.
If the 25mm/16mm tail kit is in place (and there will be suitable DP switched fuse after the meter) I don't see a problem.
Yea guys this is the best scenario however the 25mm tails are already in and ceilings boarded and skimmed. The debate has gone slightly off topic and benefits of other methods are being discussed
 
Yes i agree, so by that token does a metal object have more chance of striking the CPC in a T&E than it does if using insulated/sheathed tails? s

You’ve missed the point, it is not about striking the cpc, it is about making contact with earthed metal first.
Yes there might be slightly more chance of hitting the cpc, but that’s no good if the metal object has gone through the live first and injured or killed the person holding it.

‘More chance’ doesn’t offer any protection at all.
 
You’ve missed the point, it is not about striking the cpc, it is about making contact with earthed metal first.
Yes there might be slightly more chance of hitting the cpc, but that’s no good if the metal object has gone through the live first and injured or killed the person holding it.

‘More chance’ doesn’t offer any protection at all.
I dont think ive missed the point to be honest i fully get that. But neither the T&E method or insulated/sheathed tails offer any earthed metal work.
 
Exactly, and that is the whole point. Neither offer any more protection.
 
Problem: Reliant on Overcurrent for protection against damage to tails, damage could present an electric shock risk inside the house if there is damp etc. In fact, a high ohms fault to the tails might not trip the cutout...ever, but it will make a wall or floor live if it's damp and kill someone.

Tails are not recommended to be more than 3m. Once you put an isolator inline, you're solving that.

I'd put a 100ma time delayed isolator/rcbo just after the cutout, you probably won't get perfect discrimination when rcd testing though, although some meters play nice.

And if you had a choice, it should of been XPLE25mm to cover all bases and future proofing to 100a fuse upgrade when they want a car charger putting in the garage for their diet tesla in 5x years.
 

Reply to Routing of meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
421
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
844
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock