Hi

I’m a little bit rusty on cable calcs it’s not something I’m involved with that often for various reasons, ie promodantly do fire alarms and the small works we do are incredibly small and we tend to install 4mm to be safe.

I remember seeing on here a formula which calculate the maximum length of run you could install a cable carrying a certain current

At the moment I don’t have the design current but what I do know is

1) Confirm current Ze
2) work out design current
3) confirm current supply is capable of supplying old and new circuits
4) Apply correction factor
5) Select the cable
6) Confirm volt drop
7) using resistivity calculate R1 + R2
8) Calculate Zs from info above

I’m cautious because from the bus bar chamber to the new DB is approx 150m, this is proposed to be a 160A supply

From this DB a further 20m will be a 63A supply protected by a Type D mcb, my concern is getting the cable selection right (and not go over the top) to ensure the Zs at the end of the 63A supply is low enough to comply

Could anyone offer advice on the formula?

Thanks
 

Reply to Rusty on cable calcs in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
630
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
294
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
692
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock