I

ineedhelp

Hi all

I am fitting an external socket to the outside wall of a domestic property. I am proposing dropping a cable down through the living area stud wall and then out to socket. Because there is a socket on the outside wall does this cable routed down and through the internal wall constitute a safe zone? My next point concerns same job, I am trying to interpret regs and sort of have an answer but would like a second opinion - The outside socket will be protected by an RCD however, does the cable feeding the new socket have to be protected by RCD - i do realise if the latter is true then the external RCD is not required. My interpretation is that additional sockets require RCD protection irrespective if they are safe zoned.

The chap is penny pinching and will take me town if i fit parts unnecessarily.

Your thoughts would be appreciated

Cheers Guys/Gals
 
What sort of external socket are you fitting? What sort of CU does the installation have fitted? Does the Ring Final circuit have existing RCD protection?
 
Last edited:
non protected circuitry, tnc-s system . IP Rated external socket with or without RCD protection depending on if i have to TCD circuit.
 
The way I read your situation CU without RCD protection to any circuits, you need to protect the new cable you are installing to feed the outside socket, by fitting a RCD fused spur at the point you take your new cable from, hope that sounds ok
 
Yeah, so RCD protection is required, I sort of got that from the regs but wanted to make sure.
Cheers guys.
As for bonding, it is 6mm bonding and after checking there seems to be no deterioration of the terminations everything looks fine - so bonding is ok at 6mm.
 
Goes without saying, generally always do a ZE, PFC and bonding check before quoting job - Takes a few mins and could get extra work. Cheers for the video, not seen the chap in that video for years LOL
 
Goes without saying, generally always do a ZE, PFC and bonding check before quoting job - Takes a few mins and could get extra work. Cheers for the video, not seen the chap in that video for years LOL

You know all this stuff why are you asking questions any sparks worth his salt should already know, so the question begs what's your game
 
No game here, I always air on the side of caution with sockets and RCD the circuit if not already done so at distributor box, however as i mentioned in my original post the chap will do his research after the fact and demand money back if I fit parts unnecessarily. I simply wanted others views on the situation. As for safe zoning was not sure if an outside socket would render the vertical on the inside wall a safe zone.
 
I might be reading this wrong but a outlet on the other side of a wall does not make the opposite side a safe zone if thats what you mean !

Put a FCU on the inside and then you have your safe zone plus you can switch off the outside socket !
 

Reply to safe zones in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
553
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
743
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock