Discuss Selectivity : What does it mean specifically, especially in relation to EV chargers in the UK Electrical Forum area at ElectriciansForums.net

clanky

-
Reaction score
17
Hi all, been reading around this and i have to admit ive quickly gone out of my depth as regards EV chargers. The charger in question is a Myenergi zappi which has its own internal RCD and PEN protection. So, the usual method it seems, is to fit another small consumer board and install a DP 32/40A (either a RCD/MCB/RCBO) with an SPD. Because of the zappi's internal rcd, it seems that an MCB is the preferred choice of protection for the cable to the charger due to selectivity. What does this mean exactly? and if an MCB is fitted, doesnt that mean the cable is only protected for overload and not for any earth faults? As always, thanks for the input.
 
Your question could have a long essay written to fully cover the points you raise.
The quick version:
Selectivity - make sure only one RCD trips
MCB - if enough current flows it will trip. If the earth impedance path is low enough this includes current flowing to earth. (Usually TN earthing achieves this).
An RCD might be required to achieve this if there is no supplier earth (TT earthing)

The regs may also require additional RCD protection depending on the cable type and how it’s installed. E.g Twin and earth buried in a wall would need it.
That scratches the surface off - hope it helps.
 
The situation here is a bit different to the usual selectivity case. The classic one is you have some form of protection (OCPD and/or RCD) feeding some DB from which several other circuits all have their own protection and so the goal is to make sure:
  • The feed to the DB is protected against faults and (probably) against overload
  • As far as sensible, that a fault on any of those sub-circuits does not trip the up-stream protection and so impact the other healthy sub-circuits.
In the case of an EV charger it is almost certainly on a dedicated radial circuit and so under fault conditions having both trip is not a big deal - there is a fault to find & rectify anyway. So basically you treat the EV as any other outdoor device - the feed cable has to be protected against faults and RCD protection may be needed for that (TT case, etc) and may be needed due to the risk of a penetration accident (oh-er!) if it is not SWA or similar.

Off hand I don't know what the Zappi charger specifies, but I would fit anything like that with DP RCD protection (or neutral-switching RCBO) as you would any other outdoor unit.

The internal RCD is non-standard I believe because I think it is also part of the open-PEN protection so I guess it also switches the CPC (L+N+E) on detecting a fault, whether that is a classic imbalance on L-N or something indicating a flow of current in the CPC (e.g. open PEN has said car to high voltage and some poor sod is washing it with feet on true Earth).

EDIT: Just to add check the manufacturer's instructions as some EV chargers might need a type B "DC sensing" RCD to be used at the supply point.
 
Last edited:
From the Zappi FAQ section:

  • Circuit breaker or 30mA Type A RCBO depending on local installation requirements, 32A curve B. Please note that a higher rated MCB/RCBO may be needed due to thermal derating factors as recommended by the MCB/RCBO manufacturer.
 
From the Zappi manual:

Supply Connection
The zappi device should be connected to a single-phase 230V or 240V nominal AC supply. The supply should be from a dedicated 32A or 40A circuit breaker.

zappi features and integral 30mA Type-A RCD, therefore an RCD protected supply is not required unless local regulations state otherwise.
 
From the Zappi manual:

Supply Connection
The zappi device should be connected to a single-phase 230V or 240V nominal AC supply. The supply should be from a dedicated 32A or 40A circuit breaker.

zappi features and integral 30mA Type-A RCD, therefore an RCD protected supply is not required unless local regulations state otherwise.
Agreed, but this is one of those confusing and slightly annoying situations.
It's a case of so close yet so far.
The integral device is an RDC-DD to IEC 62955, NOT an RCD to IEC 61008 or an RCBO to IEC 61009.

So unfortunately, it doesn't comply with the letter of BS7671.
I think there's also an issue in that as it's an electronic device, a power cycle (or power cut and power restoration) will reset it without user intervention.

They have slightly amended the online info now, alluding to this:

1684593373752.png


EDIT to be fair @loz2754 already mentioned most of this in post #3
 

Reply to Selectivity : What does it mean specifically, especially in relation to EV chargers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
22
Views
508
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
581
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock