sparkysteveward

I've recently installed a SELV transformer (original one was removed by a French electrician 3months ago!). Having connected the 230v supply to the 'pri' end, I haven't got any output voltage (looking for 11.5v DC). I took it back to my supplier & got a replacement but it too is showing no output voltage. Am I missing a trick (this is my first contact with SELV) or have I just managed to get hold of 2 duff transformers?
 
If its an electronic transformer like for a LV lamp then it monitors resistance of output and wont supply voltage till conditions for which it was designed are met, if you've got standard wound transformer you said your measuring d.c. output from an a.c. input, if its just a standard wound transformer then youll need a rectifier to convert to dc... you info is vague but hope it helps
 
LV lighting transformers run at high frequency and do not supply an output until connected to a load.
If you supply power to the input and just use a voltmeter across the output the will be no reading.
Easiest way to test them it to wire them up to a light and see if it works! Can also clamp one of the wires whilst on load and measure the current and using P=VI estimate the voltage.
 
As others here have hinted LV lighting "transformers" are more strictly electronic converters which contain a "free running" HF oscillator, like most oscillators they require a minimum load before there is enough positive feedback for it to oscillate, connecting a high impedance (most digital and some analogue) meter to the "secondary" or load terminals does not draw sufficient current to initiate oscillation, hence there is no (or mVs) output voltage.
 
Hi Guys,

Thanks very much for the info. Yes it is an electronic converter. I haven't applied a load as yet but from your replies, I'm sure it'll work. I couldn't believe I'd bought 2 duff converters.

Thanks again
 

Reply to Selv in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Our old Friedland chime all too often now emits a only faint "ding"- because the person at the door (usually a delivery driver) just "dabs" at...
Replies
11
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Hope this is the correct forum for this. I have a chandelier that holds 18 bulbs, it's not in use since ages ago and I was planning to restore...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock