Hi all can anyone give me there thoughts on setting of thermal overloads. I have heard all types such as set them at 110% of FLA. Set them 125% of FLA. Set them at 100% of FLA. Get running current and set them 10% above this. But I have heard a lot set them at 110% to avoid nuse tripping?

Thanks trig
 
Set standard motor controler thermal overloads at 100% FLA, not at 110 or 125%!! Just think about what you are doing by setting the thermal protection of a motor.....
 
Set standard motor controler thermal overloads at 100% FLA, not at 110 or 125%!! Just think about what you are doing by setting the thermal protection of a motor.....
Hi there thanks for replying. I was just wondering why so many people I speak to set them at 110%. Why are they setting them higher than 100% ?

thanks
 
Hi there thanks for replying. I was just wondering why so many people I speak to set them at 110%. Why are they setting them higher than 100% ?

thanks

Because most of those have little to no working knowledge of motor protection. I've even heard of college lecturers coming out with this sort of crap, which to me just goes to show the standard of some of these college lecturers today. let alone some of the scaremongering views many persist in perpetuating!!

Those 110/125% etc of FLC, stem from the era of the old oil filled dash pot overloads, they have long since disappeared, no compensation is now necessary on the modern motor overload modules of today....
 
Last edited by a moderator:
As expressed already by E54....set to FLC of motor, if you are experienced in this area then lower than FLC may be set up by knowing the running current demand of the motor - this can be used as an early warning indicator of issues like worn bearings etc etc which can be rectified immediately by changing O/L to FLC and programming a shutdown service in when more convenient.
 
Those 110/125% etc of FLC, stem from the era of the old oil filled dash pot overloads, they have long since disappeared, no compensation is now necessary on the modern motor overload modules of today....

They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%
 
They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%

Let's hope these old dash pot contactors are being maintained then. But i'm sure you're right in that there still lurking around and still filling a function, although i haven't personally seen any of them around for now for literary donkeys years....
 
They’re still out there. Most will have a plate stating the setting level. For cane duty they also provide S/C protection. Cranes are a special case where the motors are dual rated for short term and continuous running.

Thermal O/L’s set at 100%

I've only ever seen them on fuses tony, never knew they used Thermals OL'S
 

Reply to Setting thermal overloads three phase direct on line motor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hello all, I recently was asked to quote a three phase motor install within a pallet factory. To be honest, I was somewhat stumped in how to...
Replies
3
Views
2K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock