tomas

Why this shaver socket gives me 260V on the 230V's side?? I checked for voltage about 20 of them today and all gave me 260V.
Tester: Fluke 1653.

MK Shaver Socket 115&230V - NoLinkingToThis, Where the Trade Buys
 
Last edited by a moderator:
If your getting 260v on the incomming side doesn't that mean the dwelling supply is 260v??

If not, does anyone on here know if you can get back feed from a Shave socket? I thought back emf would reduce supply current.
 
Just a thought it may require load before you get the volt drop needed you are testing a transformer unloaded at the minute.
 
good thinking, it might be it, but then the voltage regulation of socket's transformer would be 13% according to this calculations:

[ (260 - 230) / 230 ] * 100% = 13%

13% seems to be a bit big, doesn't it

I will load it tomorrow and check again.
 

Reply to shaver socket 260V? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good afternoon I have recently had a bathroom makeover and had the existing shaver socket removed as I purchased a cabinet with socket enclosed...
Replies
10
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm a pretty competent DIYer and always try to follow the relevant IEE/IET regs. Recently I ordered an LED bathroom cabinet from Amazon to...
Replies
29
Views
7K
I wonder if any one can give me some advice. I live in a fairly new build house it's 11 years old. In our kitchen there is a fused spur switch on...
Replies
18
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock