Hello All

Can anyone tell me how to carry out an Earth sheath test on an SWA cable. (i think its called that).

Thanks

JS


Yes a sheath test is basically to confirm that there is no damage to the SWA cables over-all PVC outer sheath, and therefore no future corrosion problems later on, due to moisture ingress.

The test can be taken with either an IR tester or a low ohm tester. Ensure both ends of the SWA are completely isolated from any potential path to earth, and test between any earthed metalwork and the cables SWA. You can drive a temporary spike close to the cable trench run, but that's not normally necessary in runs of 100m or less. ...Any reading, will indicate damage to the PVC sheath, and will need investigating and repair
 

Reply to Sheath test? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Has anyone come across automatic strippers to pull of the sheath of a cable already in a back box. The regular ones can do it to a degree but due...
Replies
17
Views
1K
Hello Everyone. I'm surprised this subject does not get much attention. 'The elephant in the room' I refer to is the 'new rubber'. On new...
Replies
0
Views
229
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Can anyone tell me more about Twin and Earth American style? What's it's full name? NM? Is it always flat? Do you add a sheath to the...
Replies
41
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock