Good evening

A cable was loose in a ceiling void causing a short circuit this didn't trip the 10 amp 6ka type b mcb but tripped the 50 amp type b 6ka mcb that supplied that board back at the mains.

I am wondering why this occurred other than me thinking the local protection isn't very sensitive or
Functioning efficiently.

Cheers for any responses
 
Last edited:
Mcbs or rcbos will not discriminate from each other at high currents, once you get into the instantaneous section of the trip characteristic.

The let through from the downstream rcbo/mcb is almost always more than the pre-arcing i2t required for the upstream rcbo/mcb

The same is true for rcd/rcbo in terms of earth fault current
 
Good evening

A cable was loose in a ceiling void causing a short circuit this didn't trip the 10 amp 6ka type b mcb but tripped the 50 amp type b 6ka mcb that supplied that board back at the mains.

I am wondering why this occurred other than me thinking the local protection isn't very sensitive or
Functioning efficiently.

Cheers for any responses

It's pot luck which one will go first when you put standard mcbs from 6A to 63A in series with each other.
This is why submains should be protected by either fuses or MCCBs which have been properly selected.
 
once you get into the instantaneous section of the trip characteristic.
This does make me wonder if another load on the sub-main
took up mechanical free-play in the magnetic part... giving it a time advantage !
(vs free play allowing more velocity in local one )

(- or are we heading into physics of coil size-)
( -Smaller in higher current==Less inductance to overcome peak Current)
 
Julie has it spot-on.

If you need discrimination for MCB then the up-stream one has to have some additional delay (as for the type-S RCD) otherwise a high fault current can trip whichever is quickest (or both).

With a fuse & MCB you can sometimes find that for increasing fault currents you get:
  1. Small overload, few seconds then fuse trips before higher rated MCB
  2. Medium current, MCB instantaneous trip goes before the fuse
  3. High overload, fuse blows before the few milliseconds for the MCB trip
 

Reply to Short circuit bypasses mcb and trips submain mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K
Hi I'm removing an extractor fan from our WC, as it's just a toilet and sink and we never use hot water in there anyway... The extractor is on...
Replies
12
Views
4K
BACKGROUND I live in a small town where it is difficult to find ceritified electricians. In fact, electrician certification is not common for...
Replies
1
Views
1K
The bit where I cut to the chase is in bold below if you can't be bothered with the back story. Changing MCB in main house DB for garage supply...
Replies
9
Views
4K
Have a customer who I do a lot of work for, owns several industrial units. on top of which is a large solar pv set up. Changed the 3ph DB for him...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock