Question regarding shower circuit designs. How so many times I see 6mm t&e cables supplying shower circuits on a 40amp MCB ? So for example if you were carrying out a EICR and you noticed a 6mm t&e cable on a 40amp MCB, 8.5kw/9kw shower would you put this down as a C3 or would you not put anything at all ? Giving that you don’t know how the cable is installed ? I have came across a few that when inspecting the cable has came from consumer unit up through floor floor boards and up inside external wall/pipe duct. Run approx 18 to 20meters. Now with not knowing the installation method if tangled in insulation in wall or bunched under the floor boards. Going with current carrying capacity 6mm good for 47amps but add in the factors could bring this down. Do you quote customer for changing MCB or do you make note of it on test sheet, or just leave as is ? Would like to hear other opinions ??
 
How can you change the mcb to a 32 amp mcb if the shower is either 8.5 or 9.5kw?
No evidence of thermal damage, I leave it depending on what I believe the ccc of the cable is and it is not subject to overload conditions.
Remember overload protection can be omitted for fixed loads like showers but the ccc of the cable must be suitable for the load and you must have adequate fault protection in accordance with section 434.
There are certain limitations to carrying out an EICR in which you cannot overcome.
Inspect the cable where you can, if it’s been in service for quite a number of years and has no obvious damage to it , insulation resistance test results are good, I see no reason to code it anything.
 
Last edited:
Hi Ian1981
I was thinking that the shower ratings will prob not get up to current levels where it would trip a 32amp MCB so was thinking of installing a 32amp. As regards to install, the cables run in the attic space is only where I can see any exposed run there is insulation in the attic space but these cables have been run along side the insulation and at points under but only for short run of say 600mm or so. They have also extended cables with through crimps must have been when they dropped the ceiling. The reason for doubting is I don’t know if coming up external wall there in long runs of insulation, then if they totally insulate the loft at any point this then brings the current rating down. Mostly I would only ever put a 6mm on a 32amp RCBO/MCB but if your having to state to client that this has change and pay extra for MCBs ?
 
Hi Ian1981
I was thinking that the shower ratings will prob not get up to current levels where it would trip a 32amp MCB so was thinking of installing a 32amp. As regards to install, the cables run in the attic space is only where I can see any exposed run there is insulation in the attic space but these cables have been run along side the insulation and at points under but only for short run of say 600mm or so. They have also extended cables with through crimps must have been when they dropped the ceiling. The reason for doubting is I don’t know if coming up external wall there in long runs of insulation, then if they totally insulate the loft at any point this then brings the current rating down. Mostly I would only ever put a 6mm on a 32amp RCBO/MCB but if your having to state to client that this has change and pay extra for MCBs ?
you can only code (or not) the installation as it is at the time of inspection. future possibleaddition of insulation is irrelevant as it may never happen. you are inspecting the installlation as it is, not as what it might be.
 
Yeah, good point. Just doesn’t seem right leaving 6mm cables on 40amp MCBs have never installed them like that so find it hard to leave them like that but you see them all over installed like this. Even seen new installed circuits to showers in 6mm when you wouldn’t think to install like this.
 
If the shower is either 8.5 or 9.5 kw as you said, then the load current will always exceed 32 amps unless there’s an eco setting on the shower and it stays on that setting.
All the temperature dial does is increase the flow of cold water, the current demand remains the same, depending on what the resistance of the heating element is.

A lot of electricians seam to have an issue with a 6mm2 cable being protected by a 40 amp ocpd,why?
The question is , For a shower circuit is the cable adequate for the load of the shower?
The load of the shower could be 36 amps, the ccc of the 6mm could be 38 amps, the ocpd needs to be at least 40 amps.
This set up is acceptable as the load is fixed and the ccc of the cable is acceptable for the loading of the shower.

Cables going through insulation need correction factors as per table 52.2, as an example a cable passing through insulation covered more than 400 mm has a derating factor of 0.51, so the ccc is just about halved so this presents an issue.
Are the cables/conductors that are crimped and extended covered by a suitable enclosure?
 
Last edited:
Hi yeah the crimp connections are in a suitable enclosure inside a pattress box with 1gang front plate. Im prob getting more on the side I’ll change them for. 32amp MCB that way the cable is protected ?
 
Hi yeah the crimp connections are in a suitable enclosure inside a pattress box with 1gang front plate. Im prob getting more on the side I’ll change them for. 32amp MCB that way the cable is protected ?
Can you clear the insulation away from the cable(s)?
A 32 amp mcb will be subject to constant overload conditions whenever the shower is in use.
Can you clamp the Line or neutral conductor to see what the shower is pulling?
 
I could head back and get this cleared away once this lockdown has passed. As they are occupied top flats. I think if I go and do the calculation with the section of 600mm of insulation then Current carrying capacity will be below 40amps. Might be best to run shower full blast and clamp cable to see how much it is pulling ?
 
I could head back and get this cleared away once this lockdown has passed. As they are occupied top flats. I think if I go and do the calculation with the section of 600mm of insulation then Current carrying capacity will be below 40amps. Might be best to run shower full blast and clamp cable to see how much it is pulling ?
I mean yeah by all means see what the shower is drawing.
Dont Worry if the ccc is below 40 amps , just make sure that the ccc doesn’t drop below the current demand for the shower.
Out of interest , is this a new (ish) installation?
 
If it is drawing around 37A running (8.5kW @ 230V) and you had a 32A MCB then it would not trip in under 10-20 minutes anyway, and most folk shower for less than that.

If the issue is thermal insulation covering the cable in one short area could you simply cut the thermal stuff and pull the cable over it so it is not enclosed?

If there is no sign of thermal stress (or loss of insulation resistance on the cable) it is probably fine, after all the duty cycle on it is very low.
 
It’s an old installation, has been in for years but I think the shower was upgraded higher wattage and customer said that the shower switch stopped working once before with the Black/neutral slightly damaged so they got someone up must have been when they through crimped the cable to get more length, don’t know if this was due to overheating or loose connection ?
 
If it is drawing around 37A running (8.5kW @ 230V) and you had a 32A MCB then it would not trip in under 10-20 minutes anyway, and most folk shower for less than that.

If the issue is thermal insulation covering the cable in one short area could you simply cut the thermal stuff and pull the cable over it so it is not enclosed?

If there is no sign of thermal stress (or loss of insulation resistance on the cable) it is probably fine, after all the duty cycle on it is very low.
A 32 amp may not Tripp however it will be constantly overloaded every time it’s used which could damage it beyond its normal working capacity , and is a non compliance with 433.1.1 (i) and is completely unacceptable. Regardless if you shower for 5 minutes or 20 minutes is besides the point
 
A 32 amp may not trip however it will be constantly overloaded every time it’s used which could damage it beyond its normal working capacity , and is a non compliance with 433.1.1 (i) and is completely unacceptable
Sorry, I should have made it clear that I am not suggesting a 32A MCB is a good idea, just that that it is not going to make a difference to cable protection in this scenario (i.e. cable would see the same sort of heating cycle as shower use probably below trip point).

Only real solutions are:
  • Make sure the existing 6mm cable is not too thermally insulated
  • Replace cable with 10mm or similar
  • Replace shower with lower power version
First option may be OK if it can be seen where it runs, third option probably unacceptable to the end user.
 
and bear in mind that the BS7671 figures for ccc are pessimistic. some time ago, with a 63A MCB welded closed due to a load of 110A to a pub kitchen DB fed with 16mm T/E,, i clamped the 16mm @ 104A (+/-3A) for 30 minutes. temp of the 16mm T/E reached 40 degrees C. after 30 minutes of 100+A. yet it's only rated for 80A.
 
It’s an old installation, has been in for years but I think the shower was upgraded higher wattage and customer said that the shower switch stopped working once before with the Black/neutral slightly damaged so they got someone up must have been when they through crimped the cable to get more length, don’t know if this was due to overheating or loose connection ?
Loose connections are usually the reason, not just inadequate installation torque but also thermal cycling or vibration over time. But damage can extend quite a bit back so rarely is there enough slack to fix it without some sort of replacement or extension.

Where is the joint? Is it where there might have been an isolation switch or a pull-switch for the system originally?
 
Yeah the joint has been put in the loft, on the switch wire side my guessing is that the switch was short and tight going into connection which caused the neutral to come loose and get slightly damaged on insulation. I would have thought that other conductors would see damage if this was anything to do with current carrying capacity but they never mentioned the other conductors just the neutral became damaged? So if I was to get back into attic to clear away insulation then would be a better set up rather than changing MCB out for 32amp where it could be overloadeded all the time ?
 
Yeah, good point. Just doesn’t seem right leaving 6mm cables on 40amp MCBs have never installed them like that so find it hard to leave them like that but you see them all over installed like this. Even seen new installed circuits to showers in 6mm when you wouldn’t think to install like this.

You aren't carrying out an EICR based on what doesn't seem right to you, or how you prefer to install things, you are carrying it out to BS7671.

Do you recommend that every MCB be downrated just in case the cables are in insulation? Why are you focusing on the shower circuit for this when any other circuit could be similarly affected?

You also seem to have missed the point about the CCC being permitted to be less than the MCB rating due to it being a fixed load an overload protection not being required.
 
The reason I’ve focused on the shower is that I have never put 6mm t&e on 40amp MCB when I’m newly installing only on 32amp MCB.


You also seem to have missed the point about the CCC being permitted to be less than the MCB rating due to it being a fixed load an overload protection not being required.

yeah sorry have missed that point ?
 
The reason I’ve focused on the shower is that I have never put 6mm t&e on 40amp MCB when I’m newly installing only on 32amp MCB.


You also seem to have missed the point about the CCC being permitted to be less than the MCB rating due to it being a fixed load an overload protection not being required.

yeah sorry have missed that point ?

As I said, you are inspecting to the regulations, not to your personal opinion. Just because you've personally not used 6mm for a 40A supply it doesn't mean that it is unsafe to do so.

Overload protection may be omitted for fixed loads which are not subject to overload,
 
His point is the MCB can provide only fault protection (i.e. not overload as well) for the cable to fixed loads.

The fundamental aspect is the shower load is too much for the cable if it is thermally insulated. Changing the MCB is not going to alter that situation, and would only add another part that would be overloaded under normal operations.

So the real issue is the cable getting too hot due to thermal insulation? That may be hard to check [in any sane way] if you can't inspect enough to know the typical route. But if you can see sections and they show no sign of thermal stress it should be OK.

If it is a risk then the best option would be to replace the cable with a higher capacity one.
 
This is an issue doing periodics as in most situations it is not possible to verify the full installation method of the cable. According to Table 4D5 unless you can confirm Reference Method C can be applied then 6mm cable is undersized for an 8.5kw shower. That's how I read it.
 
This is an issue doing periodics as in most situations it is not possible to verify the full installation method of the cable. According to Table 4D5 unless you can confirm Reference Method C can be applied then 6mm cable is undersized for an 8.5kw shower. That's how I read it.
I don’t fully agree as for all you know the cable has been installed correctly during the original install.
If there’s no evidence of damage and the circuit has been in use for years as is the case with this situation (red and black coloured conductors) then it’s pessimistic to give it a potentially dangerous code without evidence of any danger present or potential danger.
That said I think the OP has indicated they has been alterations done to the original circuit.

I think that the reference method on an EICR which you record can be a bit pointless tho as you said, it’s sometimes impossible to verify, but we could end up applying that scenario to every circuit present including ring final circuits that may have the ccc below the required 20 amps minimum but I wouldn’t code that without evidence of thermal damage or insulation present surrounding the cables.
[automerge]1587121839[/automerge]
To be honest, if it’s ran up the pipe boxing (which is dubious) I’d be tempted to give it’s reference method as method B
 
Last edited:
if it's in soil pipe box then it's gotloads of free air around it, unless some muppet has fille the box with itchy-poo. i'd class it as ref. C.
 
so what about cables in the voids between floors.? surely these aren't B. i'd class then as in free air, unless clipped to joists, i.e C.
 
so what about cables in the voids between floors.? surely these aren't B. i'd class then as in free air, unless clipped to joists, i.e C.
According to Table 4A2 Method C applies to cables fitted direct to walls and ceilings, in masonry walls and cables on unperforated trays. Strictly speaking according to this Table cables in floor voids would be Method B.
 
I am dealing with a similar case just now. A house I own and rent out was due for its 5 year EICR. While doing the EICR I asked the tenant if there was any problems with the installation, just the shower they said, if two people have a shower one after the other or the daughter is in it for a while it trips out. Turns out the tenant had up graded the shower without my knowledge to a 8kW on a 6mm cable with 32A MCB. I know the cable is clipped in the floor void then up inside an uninsulated lath and plaster wall and there is no sign of any distress at the connections so I am going to change the 32AMCB to a 40A RCBO once the current madness is over.
 
Yeah looking at table 4D5 it should be reference method C clipped direct. As the cable is not in 100mm insulation in wall. I think that will be best option remove any insulation around the cable in attic away and check electrical connections for any damaged insulation/over heating etc. That way don’t have to change 40amp to 32amp In Case of potential constant overload and I have made the current rating of the cable better with clipped direct and check that there is no signs of over heating ? This like said will get done when current climate get back to normal
 

Reply to Shower circuit design supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
697
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
491
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
522
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
695
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock