Scotchydog

Hi

im not to clued up on downlights but have changed the whole house to led every spot light in the house is gu10 which is great but in my bathroom 5 are GU10 an the shower extractor is MR16 the problem is she wants them to dim - just wondering what I do next do they even do a gu10 extractor downlight - what is the best thing to do?
 
Manufacturers tend to go for the 12V option for shower/ extractor lights as you are pulling wet air past the lamp and dripping water could be a problem.
However in your case there is no reason not to fit a dimmable LED driver in place of the existing transformer, the worst problem will be getting a matching colour of LED. (oh yes and trying to disentangle the transformer from the fitting in some cases)
 
Thanks for your reply - yeah I thought so I have managed to find one at same colour and yeah I understand I have to change the tranny what I'm wondering what would it be like to dim with the rest would it be totally different and look to out of place?
 
Dimmable GU10s and dimmable LED drivers are likely to use similar technology to allow dimming, the electronics in the GU10 may be a little more simple but i would expect that if you get the Gu10s dimming OK then the driver should follow that, I would limit the dimming range as much as you feel you can as it will be at the extremes that things would start to go out of synch.
 

Reply to shower extractor downlight - can you get them in GU10 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
683
Hi all, Getting the utility room redone at this project house and the misses is absolutely adamant she wants downlights. Couple of reasons for...
Replies
26
Views
2K
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
731
Hello everyone, I hope nobody minds that my first post is a question. We have a bit of a situation brewing at home with regards to our new...
Replies
38
Views
4K
Hi, I’ve had some great advice here in the past and hoping you guys can help me out again with two questions I have re dimmer switches :) I have...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock