Discuss Shower Flow Sensor + Extractor in the DIY Electrical Advice area at ElectriciansForums.net

jshailes

-
DIY
Reaction score
3
I'm thinking of installing a water flow sensor on the shower to control an extractor fan in the bathroom. I've attempted to draw a diagram of the wiring and I was wondering if anyone would mind having a quick look over it (and probably point out all of the mistakes I've made!).

I feel a bit uneasy about the rcd. The flow sensor has COM, NO and NC terminals.. am I right in thinking the NC isn't required to be connected? And is it ok to have no neutral and earth connections between the rcd and the flow sensor?

Extractor (1).png
 
Is there a reason why you don’t have/want an rcd supplying the whole upstairs lighting circuit instead of just the fan?

The arrangement shown above will not work, live and neutral have to pass through the same rcd.

I think this is a little out of the realms of a diy job.
 
  • Agree
Reactions: DPG
Is there a reason why you don’t have/want an rcd supplying the whole upstairs lighting circuit instead of just the fan?
Thanks. That sounds a good idea. I'd read that it was important to put an rcd in because it was in the bathroom and hadn't considered it could protect the whole of the upstairs lights. I've updated the diagram.

I think this is a little out of the realms of a diy job.
Thanks for the concern, I think you're right. I suppose there's a couple of reasons I'm doing it - if I didn't attempt the job I wouldn't have opportunity to learn, and secondly it helps with coordinating the tradesmen. My plan is to run all the cables whilst the plasterboard is off, potentially connect it up but leave the circuit off, and then get an electrician in to connect/test.

Lighting CU.png
 

Reply to Shower Flow Sensor + Extractor in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
752
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi, I want to wire in a timer switch to a bathroom extractor fan. The extractor fan is currently wired to the light switch or more specifically...
Replies
4
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock