Discuss shower in downstairs on rcd upstairs in the UK Electrical Forum area at ElectriciansForums.net

i assume you have a dual RCD board. you can feed the shower from either RCD. obviously on it's own MCB at the correct rating etc., etc.
 
ok now i have a shower which is 8.5kw its a new circuit. cu is dual rcd shower is gonna be in downstairs. there is no space for the shower circuit breaker on rhe rcd which feed downstairs sockets and up stairs lights. there is space on rcd which feeds upstairs sockets down stairs lights can i connect to that one ?
 
of course you can. what size cable feeds the shower?
 
OK, then reconfigure the CU. make an extra way on the other RCD by fitting a +1 way busbar and sliding RCD2 across 1 way, cut 1 way off that busbar. can't do this if it's a starbreaker CU.
 
Your fuseboard should be wired so a mixed set-up of upstairs and downstairs circuits are across the 2 rcd's i.e Upstairs socket and downstairs lights on RCD-A and respectively Downstairs sockets and upstairs lights on RCD-B.

This is standard good design practice and has advantages in its set-up.

PS swap the circuits arounds if you foresee issues with the existing set-up and re-label with the Labelling machine you have as part of your tool kit ;)
 
Sell them some candles and some matches?

Seriously though I'd just get on with it. How many ways in the board and couldn't you just move another circuit over?
 
Oh, erm, well I thought the 'YEEHAA' at the end of it may have been a bit of a givaway that I wasn't being entirely serious. Guess that one fell flat :(
 
Guess that one fell flat :(

i'll let the tumbleweed do the talking.........

Tumbleweed_rolling.jpg

;-)
 
Which is sadder? My crap joke or the fact that you have spent 5-6 mins of your life (which you can never reclaim!) hunting for an image of a tumbleweed to help illustrate the point that my joke was crap? Hahaha.
 
10 seconds too long! Lol

Naa, seriously though, back to the topic in hand, it's the usual response isn't it?

"Tut tut tut, (fingers on chin) hmmmm, deary deary me. Well, you have quite a problem here don't you, one circuit to go in, one spare way in your DB except it's on the wrong side. The only real solution to your problem here is a complete rewire if I'm honest Mrs Smith" followed by even more umming and arring and a bit more chin scratching.

Time to dust off that ol' cheque book me thinks! Lol
 
So I've just wasted 20 minutes laughing at your 'obvious' joke and agreeing with Biff about changing the lighting circuits around in the C/U ?

Well thanks for nowt guys ffs !
 

Reply to shower in downstairs on rcd upstairs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
774
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
821
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good evening all, So been to an upstairs flat today I East ham, the entire road is terraced 2 storey building which look like a row of terraced...
Replies
9
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock