Discuss Shower overheating no loose connection in the UK Electrical Forum area at ElectriciansForums.net

Ampo

-
Reaction score
15
Hi all. Shower has melted on top left corner. I thought it would likely be a loose connections on the feed. On taking the cover off the 10mm coming in and connector block looks fine and is tight and I soon realised the burn Mark is from the live going from the block up to the top of the heating/pump canister. Connections are all tight. I have run it for 30 seconds and the live gets to hot to touch but the incoming 10mm is still cold so can only guess that it's an issue inside the heating unit that is then passing the heat down the live. Anyone ever come across this? I was just expending a simple loose neutral. Triton say there have been no recalls and were pretty uninterested. Sounds like a new unit needed but has left me curious if anyone has seen this before?
 
I'm not back home at the moment but can take a photo when I am. All you will see is the live cable going from the connector block up to a crimp on top of the heater unit (tritons live cable). The insulation has not perished but it's getting hot enough to burn through the plastic enclosure. Very strange.
 
Is the shower still under warranty?

Just because there has been no recall doesn't mean the shower won't be faulty, any make of shower can develop a fault. If it's under warranty don't remove it, check with Triton what to do. I know with Mira and Redring if the unit is faulty under warranty they come and sort it...you taking it back to supplier messes up your warranty
 
No five years old. It's all good I'll just swap it out. Just thought it was quite a worrying scenario. If unnoticed for another couple mins could have easily melted through a hole and exposed live parts. When I get a min I'll chuck a clamp meter on it out of interest
 
Definitely swap out the shower. Even if it was sat in front of me and I had time to work out what the fault was, whatever it was the answer would still be to buy a new one :)

A decent replacement is about £100, or less at trade... And my preference, for less still you can just come off the tap feeds and have a proper shower? I can't stand the electric ones!!

Just one thing to consider though, just in case it isn't the shower... Check the voltage on the supply circuit. If for whatever reason it is low then your shower will be drawing higher amps to compensate for the lower than rated voltage. I'm only saying this on the off chance that there is an obscure voltage issue which itself would need looking into. For the sake of passing a multi meter over the supply terminals you will know for sure.
 
Definitely swap out the shower. Even if it was sat in front of me and I had time to work out what the fault was, whatever it was the answer would still be to buy a new one :)

A decent replacement is about £100, or less at trade... And my preference, for less still you can just come off the tap feeds and have a proper shower? I can't stand the electric ones!!

Just one thing to consider though, just in case it isn't the shower... Check the voltage on the supply circuit. If for whatever reason it is low then your shower will be drawing higher amps to compensate for the lower than rated voltage. I'm only saying this on the off chance that there is an obscure voltage issue which itself would need looking into. For the sake of passing a multi meter over the supply terminals you will know for sure.

No it won't. The shower is a fixed resistance load. If the voltage goes down, so do the amps.
 
Yeah I'll swap it was more just curiosity. Would ent use it now anyway. I'll take a look at supply voltage. Only been here for 3 months and been meaning to do a full test but haven't got around to it. This might prompt me now. I only need the next one to last a year and then I'm having a new bathroom with shower off the combi as it's also my preference.
 
No it won't. The shower is a fixed resistance load. If the voltage goes down, so do the amps.

But wouldn't the fixed resistance draw higher amps as the voltage is reduced - the same level of resistance at lower voltage would demand higher amperage to meet the resistance surely?

As ever, I accept I might be wrong - ready to learn...
 
But wouldn't the fixed resistance draw higher amps as the voltage is reduced - the same level of resistance at lower voltage would demand higher amperage to meet the resistance surely?

As ever, I accept I might be wrong - ready to learn...
No! It's a fixed resistance load, the elements resistance will not change. So if the voltage drops then the current will drop, and vice versa.

Ohms law, R (the element resistance) is the one that will not change. I = V/R
 
Exactly. Fixed resistance doesn't equal fixed current draw. With lower voltage it has the potential to carry more amps was my way of thinking :confused:
It's Ohm's law - I = V/R

R is fixed so as V gets lower, so must I.

You can think of it as the voltage pushing the current through the resistance. A lower voltage means it pushes less current through.

If you run some examples with say a resistance of 10ohms and voltages of 240 and 220, you'll see the current drop.

Edit: beaten to it!
 
Last edited:
No! It's a fixed resistance load, the elements resistance will not change. So if the voltage drops then the current will drop, and vice versa.

Ohms law, R (the element resistance) is the one that will not change. I = V/R

It's Ohm's law - I = V/R

R is fixed so as V gets lower, so must I.

You can think of it as the voltage pushing the current through the resistance. A lower voltage means it pushes less current through.

If you run some examples with say a resistance of 10ohms and voltages of 240 and 220, you'll see the current drop.

Edit: beaten to it!

Ok, I accept the weight of opinion and I'm off to google until I've got my head around this :cool:

On this basis then, lower voltage would mean lower amps so that the element would put out less heat?

My confusion comes from us once plugging an electric pool heater made in the UK, into a 220v system overseas and the cable quickly overheated. Why didn't the cable stay cool and the heater simply perform less well than it would at 240ish volts? It was a ~56a heater of a 63a supply.
 
Ok, I accept the weight of opinion and I'm off to google until I've got my head around this :cool:

On this basis then, lower voltage would mean lower amps so that the element would put out less heat?

My confusion comes from us once plugging an electric pool heater made in the UK, into a 220v system overseas and the cable quickly overheated. Why didn't the cable stay cool and the heater simply perform less well than it would at 240ish volts? It was a ~56a heater of a 63a supply.

Yep, that's right-lower voltage and lower current would mean lower wattage and less heat output.

I'm not sure about your pool heater - maybe the cable just wasn't able to handle such a high current or perhaps there were other factors involved - damage in transit? Was this for the aquarium...?
 
Yep, that's right-lower voltage and lower current would mean lower wattage and less heat output.

I'm not sure about your pool heater - maybe the cable just wasn't able to handle such a high current or perhaps there were other factors involved - damage in transit? Was this for the aquarium...?

Not for the aquarium, but for a temporary pool so same thing..

The heaters are in regular use and are tested and still perform well. It was just that one location where both heaters struggled.

They became electrically hotter than they should around the cable entry. I can't accurately say if they heated the water more/less efficiently than normal as the issue was detected, and both disconnected too soon to make any judgement on that.
 
if the element is OK, then overheating of the cable in the shower could be down to a high resistance termination, either between the cable and crimp or crimp and terminal.
 
Need to dust off the old books, I think I was getting confused with the amp thing as I would be calculating say the 9.5kw of the shower where of course ohms law throws that out the window because the 9.5kw is only relevant to the expected supply voltage so less voltage less kw less amps. Have I got there
 

Reply to Shower overheating no loose connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Bit of a strange one ive been told by everyone ive called had a triton t70xr 8.5kw The water started running cold like the tco kicked in after a...
Replies
3
Views
2K
So abit of a random one. But yesterday my Neighbor asked me if I'd be able to take a quick look at their shower as it had stopped working. I said...
Replies
14
Views
2K
Hi guys, first time posting, please bare with me! I have an old test chart as shown in the pics that i would like to get running. Everything...
Replies
3
Views
874
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock