It seems that's 8.5kw is in the middle of 6mm and 10mm so I'm stuck there. Also my C/U is in a bit of a state so while I save some money to get it upgraded I was thinking of playing it safe with an RCD UNIT along the way. And the attic is quite clean and space for it to go in there.

What are your thoughts 🤔
You should not be installing an RCD unit 'along the way'. Change your CU for an 18th edition metal clad RCBO SPD protected board, before any other DIY electrics. If you can't do that properly don't electrocute your shower
 
The conductors aren't solid, so it's bigger than 2.5mm
Probably 4mm, the wago 221s will take 6mm.

Still not 10mm, but...

Here's the post with image. While detail is difficult to ascertain, the line conductor certainly appears to be solid. Looking further into this, it's quite clear the connectors are 221-412 from data printed on them, which would accept a maximum of 4mm CSA.

I probably should have added this three weeks ago and saved you some time.

 
Still not 10mm, but...

Here's the post with image. While detail is difficult to ascertain, the line conductor certainly appears to be solid. Looking further into this, it's quite clear the connectors are 221-412 from data printed on them, which would accept a maximum of 4mm CSA.

I probably should have added this three weeks ago and saved you some time.

Conductors don't look solid to me.

And I can't see 221-412 they could be 221-612 which take 6mm


Don't actually know how i got to reply as i was looking at new posts.
 
Conductors don't look solid to me.

And I can't see 221-412 they could be 221-612 which take 6mm

They can not be 221-612 as they're printed with data found on 221-412. If you don't believe me take one of each and compare, but this point isn't up for argument as the image is clear enough to rule out any debate.

If we look back in the other thread it was made clear that the cable in question is supplied from a 16A MCB, from which the outgoing cable has an outer sheath identical in size to that seen on a solid core cable supplying a ring final circuit.

Furthermore, this is a needless distraction from the point that the cable isn't 10mm as OP believed. If you want to argue this further, then start a new thread and don't risk leading someone to believe it's fine to whack a 10.8kW shower on the end of this cable.
 
Last edited:
OP hasn’t replied to either thread since 6th September, where, on the other thread, he has fully accepted the cable won’t take a shower…


If he’s a trainee, I’m sure one of the first things you learn is that sizes are in CSA, cross section AREA, and written in mm SQUARED.
 
Furthermore, this is a needless distraction from the point that the cable isn't 10mm as OP believed. If you want to argue this further, then start a new thread and don't risk leading someone to believe it's fine to whack a 10.8kW shower on the end of this cable.
nobody led them to believe it was 10mm in fact it was the opposite stating that the maximum it could be would have been 6mm
 

Reply to Shower, what cable size and braker? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
754
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for...
Replies
25
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock