Im new as you guys know so bare with me :D

Shower is 9.5kw so thats 9.5 / 230v = 41.30 amps

6mm t+e clipped direct will carry 47amps

So on the above a 45amp MCB would be needed but you would be quite on the limit and i would personally prefer a 10mm t+e cable.


but i doubt its clipped direct more like ref meth 102* maybe ? so that means 6mm t+e will be dropped down to 35amps.
Meaning the shower would be pulling 41amps but the cable being only able to cope with 35amps if it was ref meth 102* correct ?
 
not really. think he's got the idea that 6mm cable is ok protected by a 40A , but has come for advice to confirm or reject his idea. clipped direct, the 6mm is fine on a 40A, but depending on installation method, this may be unsuitable. the only way to be sure is to know the ccc of the cable, depending on reference method, and calculate from that.
 

Reply to Shower in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock