Discuss Signed certs that are filled in badly in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
108
Morning.

A few points really and it's more due to a lack of understanding on what NICEIC will look for.

They are as followed

How critically will the inspector look at schedule of items inspected and tested?

Ie - Ze is N/V on test sheet, but ticked on schedule as tested.

If I have signed cert would it be ill advised to change the digital cert to change the tick and insert the corrected sheet?

Basically I am not sure if record information that is wrong even if the final readings are complient will be flagged.
 
Not having had much dealings withe any of the schemes, other than talking to a mate of mine who was a NICEIC QS.
The inspector should be looking a certificates with a view to ensuring the testing has been done correctly, and the certificates are filled out to reflect the test results.
 
Op what vet is it?

Not recording the Ze does sound odd.

That said I'm in a house with a new CU, the Zs for the upstairs lighting is a fib, as the cpc isn't continuous from the board.

Next example is an EICR where the readings on the cert are way different to the ones I checked

Not good
 
Op what vet is it?

Not recording the Ze does sound odd.

That said I'm in a house with a new CU, the Zs for the upstairs lighting is a fib, as the cpc isn't continuous from the board.

Next example is an EICR where the readings on the cert are way different to the ones I checked

Not good
I agree Mate, not good at all, probably get some earache, but do you think, like I do that the blame for Shoddy EICRs etc, lies with poorly trained electricians, or cheap and cheerful testing just to get the customer to stump up his cash, who will be blissfully unaware that the cert he has been given is only good for hanging on a nail in the outside Lav.
 
It's the EIC with the completely ficticious Zs that annoyed me.

I did an estimate after looking at said EIC and I didn't factor in 3 hours investigating the lack of earth on the lighting circuit.

Edit. I'm tempted to send the cert to Napit and highlight the issue ...
 
Morning.

These are often commercial jobs, so I understand why the Ze could be a limitation. However the schedule of tests show it as tested (a tick)

These certs were signed before I was taken on, but you could argue that a badly filled cert signed isn't complient. I don't want to alter and counter sign if this will cause more trouble, but equally if not correcting them is worse then I want to know I wont get stung.
 
Nominal voltage to earth 415 v ,doubtful I would bet.
Plus it's 400 v nowadays isn't it, or that's what we write in.
What about the 3 phase 3 wire? Or the no Ze, but the have confirmed the continuity of the main earthing and protective bonding conductor.

They have listed the supply characteristics but on the tick list it's N/V
 
I have certs going back 18 months because the old PDH and QS put the NIC off 3 times. They both left and I am now trying to put things right.

I can't believe more than 1 person put their signature against this.
 
It's the EIC with the completely ficticious Zs that annoyed me.

I did an estimate after looking at said EIC and I didn't factor in 3 hours investigating the lack of earth on the lighting circuit.

Edit. I'm tempted to send the cert to Napit and highlight the issue ...

That's nowt. I had a cert once that had RCD trip times on it for the kitchen alterations. Existing Bs3036 board in place with no RCD in the entire house.
How they thought that wouldn't get noticed .......... ?
 
Badly filled out certificates are very common unfortunately.
In your case I would say that you are not responsible for work done before you were appointed, however if the NICEIC are assessing a period which pre dates you then they could be unhappy, however their approval is for the future and so long as what you are doing is correct then they should be able to permit continuation.
Modification of finalised paperwork is not a good idea, reissuing the paperwork with the correct results and recording this action would be a better way of proceeding as this maintains a paperwork trail which would normally be needed for quality assurance (ha, ha!)

I have just done an EICR where there was previous paperwork, which is not common, and I found that my test results matched the previous values; this has never happened to me before and I am quite surprised to find an accurate previous assessment. It makes the job a lot easier if things are correct as Murdoch
has pointed out in reverse.
 
I noticed a mistake on one of my certs just in time.

I had used autofill and for some reason had a 6mm T&E protected by a 100A bs88 type II. Idiot...

I had to drive back home and do it again as the DNO were connecting to it in the morning. :(
 
That's nowt. I had a cert once that had RCD trip times on it for the kitchen alterations. Existing Bs3036 board in place with no RCD in the entire house.
How they thought that wouldn't get noticed .......... ?
Was there an SRCD or RCD FCU?
 
I had a cert placed in front of me as Q.S. I could see it was completed by my old boss but a flat with four rooms on circuit cable 1.0/1.0 T + E R1 + R2 =0.01 ohms total B.S.
 

Reply to Signed certs that are filled in badly in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Companies like chekatrade, homeserve , BG and other insurance products exist because of the fear that rogue traders exist I recently called an...
Replies
6
Views
1K
Good morning, Ok so this is something that has been bothering me for some time now and seems to be somewhat of a 'grey' area, I am hoping the...
Replies
6
Views
2K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
B
Hi all, I'm a spark working for a London firm and one of our clients has recently had an independent inspector in to view our work and our...
Replies
5
Views
1K
Octopus
O
I've been asked to do a couple of jobs at a potential customer. Will be taking a look tomorrow. One job is signing off others work for an...
Replies
37
Views
4K
K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock