Discuss Silly question from a newbie in the UK Electrical Forum area at ElectriciansForums.net

S

sparky in training

Hi All

I am quite new to electrics and I am still earning but wanted to ask about extending a ring final circuit using crimps. In order to do this am I right in thinking that the new socket would need to have 2.5/1.5 t&e run to the an existing socket. Remove one of the existing wires and crimp to an incoming wire from the new socket. Put the other incoming wire into the terminal where the old wire has been removed. (obviously same process for neutral) I am sorry if I have worded this in a weird way. I will see if I can do a drawing and upload it.) I know the junction box method is an alternative but I saw a socket use crimps once and it looked like a lot was going on at the back box!

Sorry if this is a really basic question
 
I have uploaded a crude drawing, hopefully trying to explain what I mean

drawisland.png
 
Yes this is a possible method of managing to extend the ring without just having a spur, there is not a lot of room in a back box to do this but it is possible and may be employed if there is no alternative.
Don't forget the earthing!

Ring extension in socket back box.jpg
 
Agree, use inline push-wire splices or Wagos in preference to crimps, if wired in T+E. Most insulated crimp terminals that you would buy over the counter make a poor connection to solid conductors. There are special types designed for the purpose but you need the dedicated tool and die set. You will see ordinary crimps used, mainly because some 'electricians' seem remarkably unconcerned about making good connections.

Don't forget to make sure the CPC of the through-connection is completely insulated so that it doesn't contact the back box. Although this would not compromise safety, it might show up as a fault during testing.
 
Agree, use inline push-wire splices or Wagos in preference to crimps, if wired in T+E. Most insulated crimp terminals that you would buy over the counter make a poor connection to solid conductors. There are special types designed for the purpose but you need the dedicated tool and die set. You will see ordinary crimps used, mainly because some 'electricians' seem remarkably unconcerned about making good connections.

From what I've read on here, other forums and the web, you could base a whole weekend conference on that very subject :)
 

Reply to Silly question from a newbie in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
891
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
722
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock