Discuss Single pole rotary isolator in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi everyone,

I have moved into a property with a 63a single pole rotary isolator controling a inline water heater. Is this safe? Surely it should be a 63a two pole isolator switching both the live and neutral?

Any advice would be much appreciated.

Thanks.
 
Most certainly NOT a single ! Is this a rental or you have purchased ?
Purchased.
It has the earth and neutral terminated within the isolator just the rotary switch is disconnecting the live only when isolated.

Just thought a high current appliance should isolate both live and neutral when in the off position.
 
a high current appliance should isolate both live and neutral

The current is unimportant, as you can get just as bad a shock from a 6A circuit as a 60A. On a domestic single-phase circuit, an isolator (which you would turn off to enable maintenance, for example) is expected to break all conductors with a 3mm contact separation. A control switch need only break the line, so is it possible that this was the intended purpose of your rotary switch, and the means of isolation (if required) is something else?
 
The current is unimportant, as you can get just as bad a shock from a 6A circuit as a 60A. On a domestic single-phase circuit, an isolator (which you would turn off to enable maintenance, for example) is expected to break all conductors with a 3mm contact separation. A control switch need only break the line, so is it possible that this was the intended purpose of your rotary switch, and the means of isolation (if required) is something else?
Thanks for your reply, I would imagine the rotary switch would be used for maintenance as the only other way to isolate the water heater would be from the 50a MCB at the board. Perhaps I am wrong and it is just used as a control switch.

So for use as an isolator for maintenance it would need to break live, neutral and earth?
 
Thanks for your reply, I would imagine the rotary switch would be used for maintenance as the only other way to isolate the water heater would be from the 50a MCB at the board. Perhaps I am wrong and it is just used as a control switch.

So for use as an isolator for maintenance it would need to break live, neutral and earth?
Never break the cpc!!!!!
 
I'd be surprised if it is a Single pole rotary isolator, more likely a Double pole but only one pole used so shouldn't be too hard to rectify.
Any pictures of the internals?
 
Sorry I meant break all live conductors, not protective ones. Earthing must never be switched
 
I'd be surprised if it is a Single pole rotary isolator, more likely a Double pole but only one pole used so shouldn't be too hard to rectify.
Any pictures of the internals?

IMG_20230404_132711_HDR.jpg
IMG_20230404_132722.jpg


IMG_20230404_132736.jpg
 
Last edited:
I don't think it's that the switch isn't DP, more that the neutral is just bypassing the switch.
 
The way I read 464.1 and 461.2 I'd say, if a TNCS or TNS supply, the requirement is only for single pole isolation.

It's an interesting point; from the point of view of final circuits controlled by a DP main switch or RCD in the CU, does the presence of a switching pole in the neutral negate the 'reliably connected to earth' that would otherwise be implied by the ESQCR? (Such DP switch being required by 462.1.201).
 

Reply to Single pole rotary isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
762
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
571
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
237
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi i have a hot tub job coming up and will need a rotary isolator. I need to bring two 6mm swa's (single phase) into its base and will use...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock