Search the forum,

Discuss Single pole up front RCD in the UK Electrical Forum area at ElectriciansForums.net

Deleted account

-
Esteemed
Arms
Reaction score
2,756
Situation.

Domestic TNS

Main consumer unit fed direct to incoming.

it has an upfront single pole RCD works fine. No main switch. No double pole isolation available.

Is this a potentially dangerous situation due to single pole Isolation?

I feel I can’t bring myself to give a C2 on an EICR, but equally I want to Tell customer to remedy this.

also it’s a Hager RCD in a steeple board, but the fit is good so was not going to code that.

bad design. Yes. But bad Design isn’t worth a code.
 
When I tripped the RCD the line to neutral on the supply side obviously 230:volts.

on other side obviously no voltage.

but between incoming live and neutral on the other side 230volts,

so came to the conclusion the neutral was open.

however ive just realised what a berk I am of coarse the neutral on the inside is connected to the neutral bar which in turn is connected to multiple circuits some of which will have natural and designed earth leakage. Thus an alternative path to earth.
 
I was getting full 230 volts.
Interesting, that is beginning to sound a bit more serious.

While I would very much doubt that an incomer style RCD would be single-pole switching, it is not beyond possibility that one pole has stuck.

I guess you could check for N-E faults on the installation (though I would expect that to be RCD-tripping if an actual short and not a few kOhm or similar from wet dirt).
 
Interesting, that is beginning to sound a bit more serious.

While I would very much doubt that an incomer style RCD would be single-pole switching, it is not beyond possibility that one pole has stuck.

I guess you could check for N-E faults on the installation (though I would expect that to be RCD-tripping if an actual short and not a few kOhm or similar from wet dirt).
my Bad my approved voltage indicator is just reading extra low voltage. just lighting up,the 12V led .

Your spot on right.

i heard the continuous tone saw lights on voltage indicator light up and presumed it was 230V.
 

Reply to Single pole up front RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
On a test & inspection today, I came across an older Wylex split load board that had been modified to add RCD protection for all circuits (see...
Replies
6
Views
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock