- Reaction score
- 2,756
Situation.
Domestic TNS
Main consumer unit fed direct to incoming.
it has an upfront single pole RCD works fine. No main switch. No double pole isolation available.
Is this a potentially dangerous situation due to single pole Isolation?
I feel I can’t bring myself to give a C2 on an EICR, but equally I want to Tell customer to remedy this.
also it’s a Hager RCD in a steeple board, but the fit is good so was not going to code that.
bad design. Yes. But bad Design isn’t worth a code.
Domestic TNS
Main consumer unit fed direct to incoming.
it has an upfront single pole RCD works fine. No main switch. No double pole isolation available.
Is this a potentially dangerous situation due to single pole Isolation?
I feel I can’t bring myself to give a C2 on an EICR, but equally I want to Tell customer to remedy this.
also it’s a Hager RCD in a steeple board, but the fit is good so was not going to code that.
bad design. Yes. But bad Design isn’t worth a code.