Morning all,
Possibly a simple question But a mix of doctor prescribed medication and post Wembley joy have left my brain elsewhere.

I have a sub DB that needs the supply isolating if a fire is detected (commercial Kitchen) So The 3 phase supply for this DB needs a 4P contactor. Do I size the contactor to the current load of the sub board(10A) so Say a 20A contactor.
Or do I need to size the contactor to 63A same as the Sub DB main switch?

Thanks Chaps...
 
Sorry, I've given the wrong info already. 63A breaker supplying new sub board with 80A main switch.

Put a 63A contactor in then. probably around the same price anyway for a 20A or 63A 4pole contactor.

Edit: I didn't insert the skim link...you can get a 63A 4pole contactor for around £25-£30.
 
Last edited:
As above you need to know your load types IE resistive/inductive AC1/AC3 respective, the price different can be 2-3 times but get the wrong contactor and it may be damaged when operating under load. If in doubt or you have a high Inductive nature to the loads then fit a 30kw AC3 contactor with a coil rating of your choice dependent on the control voltage.
 
Clearly, the 'safe' thing to do is to size the contactor to the rating of the OCPD of the distribution circuit. This is probably the pragmatic thing to do if the additional cost for a higher rated contactor is small.

However, if the sole purpose of the board is to supply the kitchen ventilation system, which comprises several known fixed loads, I would not think it wrong to size according to the actual load current. If there is the possibility of overload, one could consider rating to the sum of the OCPDs in the board, especially if there is no possibility of adding more ways.
 
Clearly, the 'safe' thing to do is to size the contactor to the rating of the OCPD of the distribution circuit. This is probably the pragmatic thing to do if the additional cost for a higher rated contactor is small.

However, if the sole purpose of the board is to supply the kitchen ventilation system, which comprises several known fixed loads, I would not think it wrong to size according to the actual load current. If there is the possibility of overload, one could consider rating to the sum of the OCPDs in the board, especially if there is no possibility of adding more ways.

That's Where my confusion was coming in, I know the load, etc So was initially planning to size the contactor to that, But with it being a commercial kitchen the chance of someone adding a fairly high load item of equipment is always a threat.
So I've sized it to the OCPD. As you say, To be safe.
 
Can you not just add a shunt trip to the breaker supplying the DB?
 

Reply to Sizing a Contactor. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Evening all, Doing a bit of forward planning for an extension with possible electric ufh. i Have worked out room will need 25m2 split between 2...
Replies
7
Views
3K
I've just carried out a periodic inspection on a building on an old RAF/USAF site. Commercial single story building. Wiring system is around...
Replies
4
Views
2K
Hi all, Little about me. new to the forum and new to the industry. I have been a data engineer for 2 years specialising in fibre but I always...
Replies
33
Views
3K
hi guys could you help me out please. I have been asked to put a contactor on a 100 amp supply to a dB on a food stand. The contactor needs to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock