Discuss Skeleton board install in Mantel cupboard and extending single insulated cables in the UK Electrical Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
Had to do a CU change in this lovely heat, so naturally it was a bit of a bugger...

Replacing a Wylex skeleton board with Type 2 breakers for a Wylex skeleton board, as client wanted it to remain hidden.

The previous board "enclosure" was made up of the nasty brown plastic front (always cracked, in my experience), a metal shelf, and the cupboard itself.

The new Wylex board fits OK, but is essentially just a standard board that hangs from the existing brackets, so leaves a gap above, which is covered by a sliding metal shield.

The cables entering the top of the cupboard all had their sheaths stripped for the original "enclosure", so if just taken straight into the new board, would leave single insulated live connectors in the gap between (albeit covered from prying fingers by the sliding shield).

Anyone have thoughts on whether the walls of the existing Mantel cupboard and new sliding shield would count as an "enclosure' for purposes of complying with regulations re single insulated cables? The shield cannot be removed without a tool (screwdriver), but is possibly not IP2X on the sides for very long fingers.

Heat sleeving was the best option that came to mind, but didn't have any on the van, so went with self amalgamating tape to reinstate the double insulation.

For future reference, any other ways people might have done it or thoughts on whether it's necessary? There wasn't room to put a separate box in the gap and extend all the wires, as I might have done in other circumstances.

Pics of the cupboard before, the new CU during wiring and the final shield. The shield was/is meant to go flat against the cover, but to do so requires removing the two screws that support the CU and since I have to go back and will be remove the cover I haven't bothered doing that)

The other cables not taped up are currently redundant wiring but left for possible access in future...

Cupboard: Cupboard.jpg

Board: Cupboard.jpg

Shield: Cupboard.jpg
 
All 3 pictures the same.

When I’ve done these the shield fits tightly so no need to tape the cables etc

Worst bit is getting that damn shelf out!

Doh! Still too hot apparently :blush: and too late to edit the post, so I'll try that again

Cupboard: Cupboard.jpg

Cover Off:Cover Off.jpg

Shield: Shield in Place.jpg


And yes the shelf was a bugger - Spot welts were done well, but a multitool flat to the top of the shelf did the trick in the end.
 

Reply to Skeleton board install in Mantel cupboard and extending single insulated cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
774
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
764
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock